Discuss Adding a spur to an existing circuit on a BS3036 CU in the UK Electrical Forum area at ElectriciansForums.net

Before you do anything make sure thr circuit you are intending to add to is in good order. As well as the other tests any good electrician would do before considering any additions to the installation.
 
All minor works you do should comply with current regs 17th edition Only the work you do has to comply with current regs not the cuircuit you are connecting to, so the socket you are installing has to be rcd protected, your method of installation inline, rcd fused fcu,rcd socket has to be used to be compliant.
Testing do a insulation res test line neutral to earth,zs at socket you are extending from ,ring end to end test to prove you have a ring main to connect to and its not a spur,if all ok away you go happy days!!
 
There should be plenty knocking about we offer one out every July but your a bit far and normally the college gives us a list of names

There appear to be plenty knocking around for those in the age range, but for those who are older than 26, there don't seem to be as many opportunities that I've come across anyway
 
All minor works you do should comply with current regs 17th edition Only the work you do has to comply with current regs not the cuircuit you are connecting to, so the socket you are installing has to be rcd protected, your method of installation inline, rcd fused fcu,rcd socket has to be used to be compliant.
Testing do a insulation res test line neutral to earth,zs at socket you are extending from ,ring end to end test to prove you have a ring main to connect to and its not a spur,if all ok away you go happy days!!

Appreciate your detailed reply. I have already done continuity, IR and Zs at socket. Now just need to decide best method of installation
 
and don't forget the 2 colours sticker on the CU, if there isn't 1 there already.
 
It appears that there is a difference of opinion as to the sense of adding a RCD FCU or one RCD socket to a non-RCD protected RFC as per a previous comment by wirepuller. Can one of the trusted long-term commenters please advise why some would say it is not a sensible way forward?

Got to learn somehow!

The regulations state that socket outlets intended for general use must be RCD protected. Where this enters into the realm of ridiculous is just the scenario you have. A 3036 board with no RCD protection to any of the circuits, and an electrician protects an isolated socket installed for a table lamp just to comply with the regulations.Despite lack of RCD protection and 3036 fuses as long as disconnection times are met and sockets are not reasonably likely to supply equipment outdoors,contrary to popular opinion the setup has been safe for decades and will be for many more. As already stated I would go with Tel's suggestion which will improve the safety of the entire circuit and be a worthwhile upgrade.
If that is not possible/customer declines cost I refuse to go down the farcical route of an RCD for one lounge socket and would just install it and label it "Not for general use".On the MW form I would state that the socket has been installed without RCD protection for a specific item of equipment.
Thats my take on it,many wont agree,nor am I suggesting it is technically the correct approach.
 
The regulations state that socket outlets intended for general use must be RCD protected. Where this enters into the realm of ridiculous is just the scenario you have. A 3036 board with no RCD protection to any of the circuits, and an electrician protects an isolated socket installed for a table lamp just to comply with the regulations.Despite lack of RCD protection and 3036 fuses as long as disconnection times are met and sockets are not reasonably likely to supply equipment outdoors,contrary to popular opinion the setup has been safe for decades and will be for many more. As already stated I would go with Tel's suggestion which will improve the safety of the entire circuit and be a worthwhile upgrade.
If that is not possible/customer declines cost I refuse to go down the farcical route of an RCD for one lounge socket and would just install it and label it "Not for general use".On the MW form I would state that the socket has been installed without RCD protection for a specific item of equipment.
Thats my take on it,many wont agree,nor am I suggesting it is technically the correct approach.
Common sense I see. I agree and the muppets who write the regs need to go back and amend them so that the installer/homeowner can jointly agree what is practical
 

Reply to Adding a spur to an existing circuit on a BS3036 CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
5K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
771
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have a working circuit setup connecting the CU to a switch and light. I want to add an additional light to this circuit, do it use the Brown or...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock