- Reaction score
- 4
bit stuck on this job got a consumer unit (in a barn) fed from a house (tns) 3 phase mcb 63 amp the zs at the barn is 0.76 but after adding a rod and making it TT managed to get zs down to 0.5. ive got to add fire alarm panel and another sub board. there will be 100ma rcd before the consumer unit but the bit im stuck at is should the fire alarm feed also be before the 100ma rcd and what about the sub sub board, its 25m away from the sub board in 16 mm armoured.... would the best thing to do to add 300ma main rcd off that add 100ma to both the sub boards then 30 ma from there ? any advice appreciated
just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board
just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board