bit stuck on this job got a consumer unit (in a barn) fed from a house (tns) 3 phase mcb 63 amp the zs at the barn is 0.76 but after adding a rod and making it TT managed to get zs down to 0.5. ive got to add fire alarm panel and another sub board. there will be 100ma rcd before the consumer unit but the bit im stuck at is should the fire alarm feed also be before the 100ma rcd and what about the sub sub board, its 25m away from the sub board in 16 mm armoured.... would the best thing to do to add 300ma main rcd off that add 100ma to both the sub boards then 30 ma from there ? any advice appreciated

just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board
 
Disconnected the tns earth and just added the rod. The zs was 0.6 sorry not 0.5... I've left it as tns at the moment on a 40a mcb until I get my head round what to do with the fire alarm and sub board. Just had a thought though. The sub sub board I could split off 1 100ma rcd with the sub board but still stuck with the fire alarm should it go before or after the 100ma rcd ?
 
ok so heres what ive got,,,,,, ze in house is 0.47,,, sub board zs is 0.73,,, sub sub board is 0.82

house mcb needs to be at least 63 amp mcb to feed the sub board in the barn,,,barn sub board mcb needs to be at least 50 to then feed the sub sub board.....the customer is really objective to having a rcd inside the house incase it trips. any body see an option for me here ?
 
Couple of questions.
What is the purpose of this outbuilding isit a leisure building, why does it need a fire alarm?
Are there any extraneous conductive parts?
What size/core swa is feeding the outbuilding?



going to be a shop
no extraneous conductive parts all plastic
its all 16mm but upgrading will be as bad as getting a new main in. so customer said no to upgrade
 
why are you trying to make it to a TT system in the barn when their is no extraneous parts in the barn?
because customer doesnt want rcd in the house so i was going to make the barn tt but while im typing this just realised my mistake, board in the house would still need rcd for fault protection. how do i get a fire alarm in the barn and get sufficient fault protection on a 63 amp breaker in the house. can i put 300ma rcd in the house after the main board then put the fire alarm on before the sub board and before 100ma rcd or can the fire alarm not go on any rcd whatsoever ?
 
I think the gyst of the thread is that the Zdb in the barn is too high for the 63a MCB although I don't have a BYB to check it. If that's the case I'd be looking to change the OCPD to a type which meets the disconnection time rather than adding RCD's where they are not otherwise required
i would need to take it to 45 amp and wouldnt be sufficient for the shop
 
From OSG table B3, for BS88-2 fuse 63A with 5sec dis we need 0.62 Ohms at ambient, leaving 0.15 to get you to the barn shop :)
 
Ok, I bet you've measured the armour as it's the cpc. If you can use a 16mm core for cpc you will get there, I think.
the cable is already in and connected ( i didnt put it in)

i need the breaker to be 63amp feeding the barn, i cant upgrade the cable, so im looking at this as putting rcd on everything( which the customer is most happiest with) but if i put rcd in the house i cant put a fire alarm in the barn shop ( <---- thats right isnt it ) is my only option to bring a new feed for the fire alarm feed from the house?
 
Understood. I'm still at trying to avoid extra RCDs etc ... I think you said it's a 4 core cable, do you need 3phase 63A in the barn or is the barn single phase? If it's single phase you can reuse a spare core for additional cpc and get the impedance down.
 
Do you need to take 3 phase over to the shop? The 50A fuse is 0.79, from the same table.
yes need 3 phase and 50a might not be sufficiant
Understood. I'm still at trying to avoid extra RCDs etc ... I think you said it's a 4 core cable, do you need 3phase 63A in the shop or is the shop single phase? If it's single phase you can reuse a spare core for additional cpc and get the impedance down.
needs to be 3 phase got 3 phase oven in barn and it feeds some 3 phase slicers
 
this farm shop you saying ,calculate the existing load before the extra load .
you need to put some pics on here to so we can see the existing supply.
candy man !

Calculate? What on earth would you want to do that for?
Just pick an MCB rating that sounds good and add a generous quantity of RCDs 'just in case'
 
Sounds if you pulled a 16mm cpc in with the sub then this would get you too your max zs value. Is this doable? Stay away from rcds & mcbs on large subs if possible for discrimination of ocpd in series during fault condition. Even if you end up TT the barn the sub would still need to meet TN disconnection times up to the isolator. Understand your in a pickle but dont get led by the customers "tight budge" as you will still need to cert your work.
 
It's a 16mm 4 core armoured. Not much volt drop at all. It's about 30 meters but that's just from r1 and rn test and rough distance

Not much at all? That's a great answer to a technical question.

A quick smoke packet calculation based on the full ratings of the ocpds suggests that your looking at 4.5V drop on the 63A submain and 3V drop on the 50A submain after that, giving a total of 7.5V drop on the submains alone.
That leaves you very little left for your final power circuits and nothing at all for any final lighting circuits.
 

Reply to Adding sub board to main consumer unit on tt in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
909
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
830
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
533
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top