Discuss Additional Kitchen ring? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi

A client is having a new kitchen installed and they have requested 8 new sockets in various places, there are currently 8 sockets installed.

The consumer unit has couple of spare ways and located in the kitchen, also Im installing downlight from below so the ceiling will be no problem to make holes etc.. I could also install majority of the new ring without removing any old units or causing much disruption for the client

I was just after some opinions whether to install a new ring main for the new sockets or just extend the existing ring main circuit. Its a 5 bed detached house and it has two existing rings..sockets up and down & kitchen and utility

All advice greatly appreciated
 
Hi

A client is having a new kitchen installed and they have requested 8 new sockets in various places, there are currently 8 sockets installed.

The consumer unit has couple of spare ways and located in the kitchen, also Im installing downlight from below so the ceiling will be no problem to make holes etc.. I could also install majority of the new ring without removing any old units or causing much disruption for the client

I was just after some opinions whether to install a new ring main for the new sockets or just extend the existing ring main circuit. Its a 5 bed detached house and it has two existing rings..sockets up and down & kitchen and utility

All advice greatly appreciated
32Amp 4mm2 Radial
 
If you install a new ring then it will be notifiable.
I don't really like the idea of having to switch off two breakers to isolate all the kitchen sockets. IMO (depending on the layout and what they are using) one circuit would be better.
 
Is the kitchen a dedicatd RFC or is it supplying other rooms in the property, is there a spur for garage etc?

I'm with Pete, a 32 amp radial would be simple enough to install.
 
Find out what is going to be plugged in. Work out what the maximum (although unlikely) current is going to be, then do the maths.
If the existing ring cable (you did say that the kitchen had it's own ring) can support the load then make sure the protective device can protect the cable and simply extend the ring.
I worry sometimes that I over simplify problems.
But it does seem to work.
 
Then consider common sense .............. a customer can only use so many appliances / accessories at once

AND go back in time and lots of houses only had 1 socket circuit and that often included the immersion.

Extend what you have.
 

Reply to Additional Kitchen ring? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Replies
3
Views
937
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock