Well here are the observations
3.5 water bonding in place but readings of 0.44 were taken C2
3.6 Couldnt be found
4.3 Plastic CU C3
4.15 The shower circuit is a 10mm t&e on a B50a MCB,
this could be downsized to a b40a or B32a C3
5.11.3 not present for circuit 1 and 2 C3
6.2.2. the isolater for the is in the kitchen C3
7.1 the top surface is not IP rated along the entire length C2
7.1 the order of circuits in the CU could be changed to a
better order C3
Kitchen cupboard, fcu not ip rated on top surface C2
Kitchen cupboard wiring is showing signs of age
and should ideally be replaced relatively soon, this
could include a partially rewire of the kitchen to remove
JB and tidy up the wiring C3
I have no idea to what cupboard they are referring to! or is it the box that contains the fuses!
3.5 water bonding in place but readings of 0.44 were taken C2
3.6 Couldnt be found
4.3 Plastic CU C3
4.15 The shower circuit is a 10mm t&e on a B50a MCB,
this could be downsized to a b40a or B32a C3
5.11.3 not present for circuit 1 and 2 C3
6.2.2. the isolater for the is in the kitchen C3
7.1 the top surface is not IP rated along the entire length C2
7.1 the order of circuits in the CU could be changed to a
better order C3
Kitchen cupboard, fcu not ip rated on top surface C2
Kitchen cupboard wiring is showing signs of age
and should ideally be replaced relatively soon, this
could include a partially rewire of the kitchen to remove
JB and tidy up the wiring C3
I have no idea to what cupboard they are referring to! or is it the box that contains the fuses!