Discuss AM I BEING TAKEN FOR A RIDE Continued....................... in the UK Electrical Forum area at ElectriciansForums.net

Well here are the observations

3.5 water bonding in place but readings of 0.44 were taken C2
3.6 Couldnt be found
4.3 Plastic CU C3
4.15 The shower circuit is a 10mm t&e on a B50a MCB,
this could be downsized to a b40a or B32a C3
5.11.3 not present for circuit 1 and 2 C3
6.2.2. the isolater for the is in the kitchen C3
7.1 the top surface is not IP rated along the entire length C2
7.1 the order of circuits in the CU could be changed to a
better order C3
Kitchen cupboard, fcu not ip rated on top surface C2
Kitchen cupboard wiring is showing signs of age
and should ideally be replaced relatively soon, this
could include a partially rewire of the kitchen to remove
JB and tidy up the wiring C3

I have no idea to what cupboard they are referring to! or is it the box that contains the fuses!
 
I will make a bit of a guess at some of those.

"the top surface is not IP rated along the entire length". Is it in reference to the top of you consumer unit having holes in it that a finger could go into (don't test it with your finger)?

"Kitchen cupboard, fcu not ip rated on top surface C2". Do you have under counter lighting ? This may be connected to a Fused Connection Unit that has holes in or is damaged.

Could you ask the electrician to physically point out the faults as you aren't clear on what it means.

Also post as many photos of your installation as you can.
 
No, I do not have any under counter lighting at all. The only thing I can think of is that he is referring to the airing cupboard where there are some switches ie the timer and the switch for the electric fans as well as the switch for the electric towel rail in the bathroom. Yes I will ask for photographs as you have said. Good idea.

Yes I think he is referring to the consumer unit. The original electrician who put in the underfloor heating put the new unit - is it also called a meter unit! - inside the old box! hence perhaps there is a space, although I didnt see one I must say. However I am happy for them to change that, although I have no idea what the 7.1's are. I looked them up on google and it seems to refer to cabling in the manual!
 
Because a lot of what he said seemed dodgy to say the least and he wanted to put in a cable from the Economy 7 through the lounge because he said that he could not test the cable for the economy 7 because he could not see it, so that sounded odd to me and so I posted on here and after that I met up with him and he removed some of the things he said were wrong. If can I help it I do not want a cable running through the lounge and why could he not test it. It all seemed strange so I wanted to get a second opinion and this electrician has come up with completely different issues! which is more then confusing to say the least.
 
I was hoping for a clear safety certificate as I got the electrician in who put in the underfloor heating in the first place to rectify some of the issues. I was only wanting this one to test the economy 7 which he failed to do because he said he ran out of time.
 
I was hoping for a clear safety certificate as I got the electrician in who put in the underfloor heating in the first place to rectify some of the issues. I was only wanting this one to test the economy 7 which he failed to do because he said he ran out of time.

"Ran out of time..." What did you pay the guy to test? Everything?
 
ran out of time means I don't have a clue and "escaped"

Well this is what they said to me in an email and I quote "

I have to apologise but the Eco 7 board was not tested due to time constraints. I have been made aware it was in the email you sent over initially and it should of been tested. I can only apologise for this and ensure it will be tested on our return".

I am sure you are right that he didnt have a clue like the first one and so that is why he came up with the idea of putting a clonking great thick cable running along the wall of the lounge into the kitchen
 
the problem here is obvious. you have been using the "services" of southern electricians, whereas a northern sparks would have had this sorted before noon, been in the pub for 1.00pm, and home in time to clout the sprogs on their return from their community service.
 
the problem here is obvious. you have been using the "services" of southern electricians, whereas a northern sparks would have had this sorted before noon, been in the pub for 1.00pm, and home in time to clout the sprogs on their return from their community service.
Southern sparks are holidaying in the Caribbean over Christmas and the New Years and should be back in time for Easter.
 
the problem here is obvious. you have been using the "services" of southern electricians, whereas a northern sparks would have had this sorted before noon, been in the pub for 1.00pm, and home in time to clout the sprogs on their return from their community service.
they like to roll up are sleeves up north, not down south.
upload_2017-12-13_13-13-23.png
just pansies.
 

Reply to AM I BEING TAKEN FOR A RIDE Continued....................... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
748
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
295
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock