Discuss Applying Diversity to separate Oven & Hob in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
I'm trying to determine the appropiate load to install a separate oven and ceramic hob (in a domestic kitchen). Obviously I will apply diversity to provide a suitably rated protective device & cable. However, I'm scratching my head on how to apply the diversity:

Is it:

1) Oven & hob total load in kw, then apply diversity = calculated load

OR

2) Apply diversity to the total load of each individually, then combine to calculate load

The OSG (table A2) refers to 10a + 30% fl of connected cooking appliances. So am I right in thinking it's 1?
 
Yes I agree with Tel too!!

Alternatively you can check the manuf instructions. They sometimes contain the loading with diversity applied --- job done for you!
 
Thanks chaps for the quick responce, I can get on with my quote now!

Manufacturer only gives total load for each appliance (4.2+6.7kw respectively), but does specify connecting each appliance with 3c 2.5.
 
Re: Applying Diversity to separate Oven & Hob

yep.good old 6mm on a 32A MCB. good for that little load.

- - - Updated - - -

but i'd use 4mm flex on the hob, myself.
 
Manufacturer only gives total load for each appliance (4.2+6.7kw respectively) said:
Fitted a nice Kenwood (?) style all electric range cooker at the week-end and the instructions had kindly given the load with diversity applied and the cable to be used to connect with ....... cant beat following manuf instructions!
 

Reply to Applying Diversity to separate Oven & Hob in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
830
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi everybody, Looking at putting a kitchen grid switch in my kitchen and wanted to see what you guys (and girls) thoughts were about my set up as...
Replies
9
Views
8K
Hi all, Looking for some advice if possible please! Got one if then jobs that you get roped in to and that’s turned from a quick simple...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock