I am interested in opinions on the following. Looking at GN3, page 126 the example of a Generic Schedule of test results lists the reference method as 100. When I look at the OSG Table 7.1(ii) on page 74 it lists A, B, C, 100, 101, 102 & 103 as 'installation reference methods'. However when I refer to BS7671 section 7.1 the reference methods are A through to G. Also Section 7, Table 4A2 for methods 100 to 103 (page 390) redirects to Table 4D5 which labels methods 100 to 103 simply as 'methods' not reference methods. So my conclusion is that GN3 and OSG do not comply with BS7671.
 
I don't have any intention of getting into a long discussion but draw attention to a few quick things.
7.1 "The reference methods are those methods of installation for which the current carrying capacity has been determined by test or calculation".
Table 4D5 does exactly that task too.

Ultimately all that matters is BS7671. As the OSG seeks to provide a condensed guide to a complex document it inevitably makes generalisations and simplifies things.
GN3's focus is I&T. Part of inspecting is determining if the OCPD is appropriate for the cable and installation method. Recording the method, whether A,B or 103 is simply showing your working.

The point of the system is to provide the most efficient way to match method/environment and cable type and end up at a number. A-G can be applied to most cable types and was deemed sufficient. I suspect that the amount of T&E out there and the variation in performance in frequently used environments caused the powers that be to create some special tables for it. For example the depth of insulation is the difference between complying with the 20A ring final circuit reg or not.

I don't really see a problem here.
 

Reply to Are installation methods 100, 101, 102 & 103 Reference methods? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys Is there a reason why installation ref method B (in conduit or trunking on a wall) not listed as an allowed installation method on the...
Replies
3
Views
839
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi everyone. What's the correct reference method for cables (2.5mm t&e 32A? ring main) clipped to wooden joists between the ground floor and...
Replies
12
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
518
I have one in the OSG and I have the BSI IET (size of a yellow pages) regs book. I found this too...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock