Search the forum,

Discuss Band 1 & 2 circuits in the same enclosure in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
This question relates to 528.1 of the wiring regs (proximity to electrical services). It states that these bands will be kept separate unless one of 6 different methods are adopted. The two exceptions im most interested in are below:

1) Every cable or conductor is insulated for the highest voltage present.
2) Each conductor of a multicore cable is insulated for the highest voltage present in the cable.

I have come across many prepayment heat metering systems where either a 5 core cable is used to take L/N/E (230V) to the prepayment unit and the remaining two conductors are used as communications (36v) between the heat meter and the prepay unit. Alternatively two separate cables are used but ran in the same trunking, both cables designed for 230v although one carrying just 36v.

Looking at the I above section of the bs7671 this looks to be ok, as far as i interpret it. I just wondered what others would say.
 

Reply to Band 1 & 2 circuits in the same enclosure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not wanting to derail the Dodgy work pictures thread but a comment was made that a fire alarm FP200 shouldn't be in trunking with 230V band 2...
Replies
10
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
542
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock