544. 1.2
“The main equipotential bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer's hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external”
Strongly implies that you shouldn’t bond at the meter box. However I do bond there if that’s the most practical place for it. Meter fitters hate it when I point out this regulation to them after I’ve bonded at the point of entry. Say where the pipe work comes out of a semi buried meter box and in through the wall to a cupboard housing the boiler.
A bit of common sense is all that’s needed
“The main equipotential bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer's hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external”
Strongly implies that you shouldn’t bond at the meter box. However I do bond there if that’s the most practical place for it. Meter fitters hate it when I point out this regulation to them after I’ve bonded at the point of entry. Say where the pipe work comes out of a semi buried meter box and in through the wall to a cupboard housing the boiler.
A bit of common sense is all that’s needed