This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?
 
Last edited:
Sorry, I may have worded it incorrectly..

I dont mean to put in a new BS3036 board. I simply mean to carry out work in a household that has a BS3036.

He has stated that if you want to add a new circuit to the electrical installation in a house which is protected by BS3036 rewireable fuses then this would be unsafe as they do not meet the 0.4s disconnection times. he has said that you would need to change the board.

In fact he said all BS3036 boards should be change as they are dangerous and do not meet the 0.4s disconnection times
 
that assessaor will be a delight to the Electrical Trainee's who want to recoup their £6000+ asap. " that's board's illegal, mrs. pensioner i'll have to replace it for £500".
 
something like:

S2606_106766_00_PP_515Wx515H.jpg
 
that assessaor will be a delight to the Electrical Trainee's who want to recoup their £6000+ asap. " that's board's illegal, mrs. pensioner i'll have to replace it for £500".

I would go as far as advising that they move out until the work is carried out for safety reasons ...
 
Some of these inspectors are self employed , and float from one scam to the other I had noticed on some paperwork once ...
 

Reply to BS 3036 fuses not allowed for new circuits!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
695
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock