Discuss BS 3036 fuses not allowed for new circuits!! in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?
 
Last edited:
Sorry, I may have worded it incorrectly..

I dont mean to put in a new BS3036 board. I simply mean to carry out work in a household that has a BS3036.

He has stated that if you want to add a new circuit to the electrical installation in a house which is protected by BS3036 rewireable fuses then this would be unsafe as they do not meet the 0.4s disconnection times. he has said that you would need to change the board.

In fact he said all BS3036 boards should be change as they are dangerous and do not meet the 0.4s disconnection times
 
that assessaor will be a delight to the Electrical Trainee's who want to recoup their £6000+ asap. " that's board's illegal, mrs. pensioner i'll have to replace it for £500".
 
something like:

S2606_106766_00_PP_515Wx515H.jpg
 
that assessaor will be a delight to the Electrical Trainee's who want to recoup their £6000+ asap. " that's board's illegal, mrs. pensioner i'll have to replace it for £500".

I would go as far as advising that they move out until the work is carried out for safety reasons ...
 
Some of these inspectors are self employed , and float from one scam to the other I had noticed on some paperwork once ...
 
Ok... so does anyone have any idea if what he is saying is correct?

Is it ok to connect up a new circuit to a BS3036? This is in relation to the 0.4s disconnection times, i.e the assessor says it does not meet them?

My answer was that it depends on the Zs as to whether the BS3036 would disconnect in time, but the assessor did not accept this.
 
Ok... so does anyone have any idea if what he is saying is correct?

Is it ok to connect up a new circuit to a BS3036? This is in relation to the 0.4s disconnection times, i.e the assessor says it does not meet them?

My answer was that it depends on the Zs as to whether the BS3036 would disconnect in time, but the assessor did not accept this.

They still disconnect the same as they always did!
 
You can use any protective device so long as you meet the disconnection times. BS3036 fuses are still listed in BS7671 so as long as the measurements and calculations work out, they are fine.
 
One thing I would say is that if you are going to extend a circuit protected by a BS 3036 fuse then the correction factor of .725 would have to be applied to this circuit . the only thing I would do is to use a fused spur to feed an additional point or RCD fused spur if required ...
 
Yep me too. If thats whats required.

HHD next time you meet that assessor, ask him how he feels about 13A fuses, and the like, as they are effectively just like a rewireable, as in, a bit of "fuse wire". Ask him if he thinks every house in the country needs a circuit breaker fitting at the service head instead of that silly great fuse wire thing.
 
You can use any protective device so long as you meet the disconnection times. BS3036 fuses are still listed in BS7671 so as long as the measurements and calculations work out, they are fine.
until some complete moron of a customer fits a nail in.
 
Late to the debate, but totally agree with the consensus, the assessor is wrong. As has been stated, if the circuit Zs falls below the adjusted max Zs value (0.87 for 30 amp, iirc), your good to go.
Oh, and ask him which Reg he is using to justify his comments.
 
In the new 3rd edition/cash cow if you added a circuit to this CU would have to add a RCD or do it surface glav or in glav in the fabric of the building or more than 50mm deep in the building. And this is the best in a building with an electrically skilled person you have to do a risk assessment to say, why you deem it safe not to have a RCD.
 
[][/B]
In the new 3rd edition/cash cow if you added a circuit to this CU would have to add a RCD or do it surface glav or in glav in the fabric of the building or more than 50mm deep in the building. And this is the best in a building with an electrically skilled person you have to do a risk assessment to say, why you deem it safe not to have a RCD.[/QUOTE]
2nd bit in bold that's just for a socket outlet without RCD protection and if the installation requires RCD protection then you would have to put it on a RCD anyway.

And the 1st bit in bold you should already be doing this anyway but doesn't have to be galv when surface.
 
Last edited:
This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?

Jesus glad I'm not one of your client using a Regs book which as been out of date for 3 years
 
One thing I would say is that if you are going to extend a circuit protected by a BS 3036 fuse then the correction factor of .725 would have to be applied to this circuit . the only thing I would do is to use a fused spur to feed an additional point or RCD fused spur if required ...

Late to the debate, but totally agree with the consensus, the assessor is wrong. As has been stated, if the circuit Zs falls below the adjusted max Zs value (0.87 for 30 amp, iirc), your good to go.
Oh, and ask him which Reg he is using to justify his comments.

Not sure what you mean by 'adjusted max Zs' Polo? Page 55 BGB has the max Zs for a 30A BS3036 as 1.09?

Are you referring to appendix 14 BGB?
 
Jesus glad I'm not one of your client using a Regs book which as been out of date for 3 years


I dont think you quite understood the sentence. I have BGB.thought the 3036's would only be in BRB
 
Last edited:
a recent poll of around 11,000 ppl came back with 80% saying get out.
 
telectrix I was talking in general with this new amendment Cmin 230vX0.95 218.5volts this is the voltage you have to calculate your ZS from now my old man is right the older u get the more bull u get. Roll on 85 and don't let the chips get u down.
 

Reply to BS 3036 fuses not allowed for new circuits!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
789
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock