HappyHippyDad

-
Esteemed
Arms
Supporter
Reaction score
5,659
This is what my assessor has told me!

He states that the BS3036 does not meet the 0.4s disconnection times and cannot be used for any new work.

I do not have a BRB so cannot see the disconnection times for a 3036.

Surely he is wrong? He is suggesting that we have to change the 3036 if we want to carry out any work.

Bit cross... I did not like him at all.. different bloke to last time!

.....

sorry, I do have the disconnection times for 3036 in the BGB...but surely it's dependent on the Zs?
 
Last edited:
Sorry, I may have worded it incorrectly..

I dont mean to put in a new BS3036 board. I simply mean to carry out work in a household that has a BS3036.

He has stated that if you want to add a new circuit to the electrical installation in a house which is protected by BS3036 rewireable fuses then this would be unsafe as they do not meet the 0.4s disconnection times. he has said that you would need to change the board.

In fact he said all BS3036 boards should be change as they are dangerous and do not meet the 0.4s disconnection times
 
that assessaor will be a delight to the Electrical Trainee's who want to recoup their ÂŁ6000+ asap. " that's board's illegal, mrs. pensioner i'll have to replace it for ÂŁ500".
 
something like:

S2606_106766_00_PP_515Wx515H.jpg
 
Ok... so does anyone have any idea if what he is saying is correct?

Is it ok to connect up a new circuit to a BS3036? This is in relation to the 0.4s disconnection times, i.e the assessor says it does not meet them?

My answer was that it depends on the Zs as to whether the BS3036 would disconnect in time, but the assessor did not accept this.
 
Ok... so does anyone have any idea if what he is saying is correct?

Is it ok to connect up a new circuit to a BS3036? This is in relation to the 0.4s disconnection times, i.e the assessor says it does not meet them?

My answer was that it depends on the Zs as to whether the BS3036 would disconnect in time, but the assessor did not accept this.

They still disconnect the same as they always did!
 

Reply to BS 3036 fuses not allowed for new circuits!! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock