Discuss Commercial kitchen from home in the UK Electrical Forum area at ElectriciansForums.net

round23

DIY
Reaction score
1
Hi,

I'd be getting an electrician to complete any work but would still like an idea first on what is and isn't possible and the best way of going about it.

In a nutshell, we are looking at converting the spare area of our dining room into a mini-commercial kitchen by mainly using electrical counter-top equipment. Already we have 4 x 5 ltr fryers (2.8kW each @ 240V) and a griddle (2.2kW @ 240V). Based on my calculation this is roughly 58A and will instantly trip the 32A breaker that the sockets are currently on.

Is it possible to increase the 32A capacity?
If so, would this be a large job involving re-wiring all downstairs sockets to something like a 6mm cable and increasing the maximum capacity of the circuit board from 100A?
Any ideas and ball park costs I would be looking at?

Many thanks
 
I would suggest a dedicated consumers unit/dis board be installed locally and feed each item separately. A small dedicated final ring circuit (socket outlets) could also be incorporated for smaller portable/low load items. This would also allow if required separate metering to allow separation of the billing between home and commercial costs. More info required really.
 
Give us as much detail as you can in terms of frequency of use,what you're likely to run when,any running at the same time, average run time of each appliance (makes/models/specs would also help). Are they going to be on constantly?

As no doubt any of my fellow members will say; speak to an electrician, draw up a design and go from there, you don't have to go with whatever the Electrician suggests but it is vital to consult one at what is effectively the design phase.

You may find a lot more is required than you think, depending on factors like loading of existing, current demand Vs maximum demand, whether or not your existing service fuse will be adequate for the additional demand.
 
I like Steve the sparks idea of a local Cu for the new kitchen but I think I’d put each appliance on a separate circuit Rather than a ring.

wiring guidelines are that appliance over 2kw should have there own dedicated supply ( separate circuit).
I did mention supplying each item separately :)
:)
That would have been the reason for the dedicated CU :)
 
increasing the maximum capacity of the circuit board from 100A
Most domestic supplies have a service fuse that can be as low as 60amp. It could be 80A or 100A. You can enquire with your DNO to find out what your supply is limited to. You can ask for an upgrade, but the maximum domestic single phase supply is generally 100amps. To go more than that would mean the installation of a three-phase supply, unless you already have one then you can ask the DNO the cost to do this. Be sitting down when you get the quote though. It may be cheaper to rent a commercial kitchen that already exists. Plenty of pubs sitting empty right now.
 

Reply to Commercial kitchen from home in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
737
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Looking for some advice on what I've discovered is the electrics situation in my rental property. I'll note that before I moved in here I made...
Replies
118
Views
11K
Hi all, I am undertaking a partial rewire of a house that a client is needing to do quite a bit of surgery on as tenant just left and what a mess...
Replies
10
Views
2K
Hello again Thanks to those who answered my question on PIR/occupancy sensors for my downstairs toilet. I have some questions regarding a flat...
Replies
17
Views
4K
specs
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock