Scenario: Commercial TPN distribution board down stream requiring type2/3 protection. Board is at full capacity and breakers discontinued etc. how are people getting around this? is it acceptable to be doubling up in the supply side of the main switch to feed separate enclosure with triple pole switch to control supply to SPD? cant see any reason why this would not be acceptable as long as ccc is met and connection is electrically and mechanically sound , interested to hear your thoughts

thanks
 
If the incoming supply is already fused at a level to meet the SPD's OCPD requirement then it seems a reasonable solution.

Is there any means of isolation before the board (if you are tapping off before the main switch)?

Can you keep the SPD cable lengths down to an acceptable distance (ideally 0.25m max for each cable so 0.5m loop L-E, etc, but certainly below 0.5m max so less then 1m loop) ?
 
Thanks for your reply , yes so the distribution board is fed from a MCCB panel board @ 63A. My plan is to match up the supply cable size , come off the incoming side of the main switch to feed a 63a triple pole MBC in a separate enclosure then loop over to surge protector all under 0.5m
 

Reply to Commercial Surge Protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
493
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
815
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock