Situation DNO supply into garage outside meter box, submain into house approx 10M in concentric cable. Fused down by 80 swfcu . I dont know the size but it has 7 neutral strands and approx same cpc strands. Any thoughts on this.? Is it ok? I would have thought ok as same if not very similar to DNO use, just unsure where it relates to concentric in bs7671
 
I too have split concentric from meter to CU in my house. Nowt wrong with it if terminated well.
That said, I am probably going to swap it out for SWA when an opportunity arises.
 
Up to and including 16mm its 7 neutral stands, 25mm 11 neutral strands. Approx overall diameter 12.9mm for 10mm, 15.2 for 16mm. With regards to being buried in walls, floors or walls made of metal portioning should be treated the same as T&E where RCD protection is concerned. With CCC I've heard its similar to SWA but most data you find online will be for 90 degree not 70 degree. Probably best to ping an email to a few manufacturers or phone your scheme tech line and let them do the donkey work :)
 
Makes sense to treat it as t&e lee. The cable disapears down through dno box buried through garden then flies in through back of cu no gland in dno box either just floats into a sw fuse! Very poor but hesitant to make a big deal of it to this new customer as may come accross wrong! But deffo poor install
 

Reply to Concentric cable used as submain? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447
Morning all, started a job yesterday fit a bathroom fan etc. When I took off consumer unit cover to do dead test I came across a split...
Replies
13
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock