Discuss Crabtree c50 code 2 or not in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C50 is a valid MCB. The only things that might make it a C2 could be if the EFLI is out of range, or that the cable(s) connected to it are not good for an Ib of 50amps.

A deviation on a report should give the regulation number that has been breached. Which one did he/she quote?
 
Utter --------.
C50 range was produced to BS3871. Exact Zs values for all types of BS3871 breakers can be found in the back of GN3. As long as they meet these values they should meet the times for disconnection.
 
A C50 is either a 3871 type 2 or 3871 type C (yes) there is no type 3. You need to check the side of each breaker if there is nothing indicating a type then assume 3871 type C but some actually state 3871 type 2 or 3871 type C. New versions which were still being made up to recently will be 60898 type C and is written on them. The colour of the writing does not indicate its type but it's ka rating which off the top of my head I cannot recall. This information will be confirmed by Crabtree and they are perfectly safe for continued use. Ignore where it states Part 1 on the side this is not a type but it's compliance with BS3871 Part 1.
 
But without reference to a regulation how can it be recorded as an observation on an eicr?
Didn't say I agreed with it but it is a fact that the proposal to require the Regulation breached to be recorded against the Observation was rejected when the final draft of BS7671 was published.
 
Didn't say I agreed with it but it is a fact that the proposal to require the Regulation breached to be recorded against the Observation was rejected when the final draft of BS7671 was published.
Since when did you have to include the regulation number on the observation sheet?

Sorry wasn't meant as a direct reply to you
 
'Twas what I was taught on my 2391. Without the qualifier of the reg number the inspector leaves themselves open to the question of "who says" and (often) "you're making it up to create work for yourself "
 
I never quote Regs. on an EICR.
What I do is state the fault and quote the appropriate Reg. No.
For instance:
Lack of RCD protection for sockets intended for general use in accordance with Regulation 411.3.3.
 

Reply to Crabtree c50 code 2 or not in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
427
I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Replies
11
Views
365
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock