Hi Does anyone know if rcbo,s available for older starbreaker boards,not the c50,i think its sb6000 range.6a type b req.
 
http://i.ebayimg.com/02/!BP2d!q!!mk~$(KGrHgoOKjsEjlLmVqugBJ1z3)C5)g~~_2.JP G
cant find individual rcd / rcbo but this is an rcd main switch if any use

will need to copy/paste link its not working prop
 
Last edited:
Only other alternative is to put the circuit (s) through a separate RCD enclosure.

Still expensive but cheaper then a new CU.
 
That is an alternative,but on this job price is king.When i explain reqs to do the work they will prob not go ahead,or use someone else.Thanks.
 

Reply to crabtree split load board. in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hi all, I needed to replace an MCB for an electric shower with a different rating, it's an older Loadstar consumer unit, and crabtree told me word...
Replies
0
Views
627
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
251
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
714
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock