Search the forum,

Discuss crawlspace cable in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
i want to run a something like a BX cable from a sub panel in my garage through an adjacent crawlspace to a fish tank in a room just the other side of the crawlspace. total length is 40-50ft. i'd like it to carry two 20A circuits which would be connected to outlets in the cabinet under the tank.
what is code to do this? and what would the best thing to do here?
 
i want to run a something like a BX cable from a sub panel in my garage through an adjacent crawlspace to a fish tank in a room just the other side of the crawlspace. total length is 40-50ft. i'd like it to carry two 20A circuits which would be connected to outlets in the cabinet under the tank.
what is code to do this? and what would the best thing to do here?
You can legally have two 20 amp receptacles on a 20 amp single pole breaker using # 12/2 MC cable. Since the receptacles will be under a sink then they will need to be GFCI protected.
 

Reply to crawlspace cable in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I received multiple quotes to install a long run for my electrical outlet NEMA 14-50 for my tesla. The cost is huge $1800 give and take...
Replies
1
Views
553
Hi, I am burying wire from the outside meter panel to the new 100amp sub panel inside a garage. The run is 20' long. Is 2-2-2 Aluminum URD Cable...
Replies
0
Views
815
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
532
DIYer here. I'd like to install an electric car wall charger myself. It calls for 6/2 romex which I have. Unfortunately my panel is in my...
Replies
0
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock