Discuss cyclinder stat blowing fuse in the Industrial Electricians' Talk area at ElectriciansForums.net

C

Chrisel

Called out by a plumber I do work for. He had recently installed a new zone valve and chaged CH/HW programmer. A fortnight later the customer calls him because he has lost all heating. Plumber turns up, realises 3A fuse has blown in switched fused spur. He can't change it without it blowing. Calls me.

The spur supplies the boiler which, as well as central heating, heats water into the tank. Spur therefore also supplies programmer, zone valve and cylinder stat. I identify the cylinder stat as the issue; we replace this. Everything starts up, we run the system. Everything is working well.

No. Two days later the customer calls the plumber, the fuse has blown again.

Before I return to the property and recover exactly the same ground, is there any advice out there as to what might be causing this. Could there be an underlying problem that I missed, causing a problem through the stat. I don't want to have to return every 2 days and install a new cylinder stat.

Thanks
 
You say the plumber installed the valve, did he do the wiring connections too?
Is it possible that the cylinder stat was temperature satisfied at time of replacement, but after you had gone the stat called for heat, there was a termination error at the wiring center, and pop??
 
Before I continue I will admit I did not carry out as thorough testing as I should have. I had just finished another job for him, just as I had packed up the van and was about to drive away "could you go and look at a problem for me..." I then had a very short window to get the job sorted out. Enough excuses....

When I started testing, nothing made sense at all, I couldn't identify any cables leaving the programmer and arriving at the junction box. I didn't want to start taking everything apart so I simply went through each step.

Disconnected the hot water side of the programmer: power stayed on. With HW ON channel disconnected everything stayed on.

Then disconnected each item on the HW side. The usual culprit I find is the pump but the fuse still blew with that attached. When I disconnected the cylinder stat the fault was removed. It was at this point I tested the cable I had disconnected at the programmer (blue) with the cable I had just disconnected (red) and realised there was a join somewhere. Indeed; on digging around I find another (hidden) junction box, which explains my initial problem with identifying cables when testing and making sense of how it had previously been wired.

We changed the stat, ran the hot water and central heating, everthing was okay.

In an ideal world I would probably return and rewire the whole thing so that there is only one 10-way junction box but we are not in an ideal world.

I was just enquiring as to whether people here have encountered a common problem with regard to cyclinder stats in order to at least give me a starting point when I return. I am quite prepared to put several hours aside on Monday to just start testing everything one by one but thought it doesn't hurt to have some advice in advance as my experience with these systems is limited
 
He did the wiring, yes. He assured me he just replaced like for like.

Anything is possible. The thing I keep coming back to is they used the system for two weeks after he made the initial changes so I find it unlikely (but admittedly not impossible) that him changing the valve caused the problem.

Similarly, it worked for two days after I was there. Having said that it has just occurred to me, they called him two days afterwards. That doesn't mean anything does it?
 
He did the wiring, yes. He assured me he just replaced like for like.

Anything is possible. The thing I keep coming back to is they used the system for two weeks after he made the initial changes so I find it unlikely (but admittedly not impossible) that him changing the valve caused the problem.

Similarly, it worked for two days after I was there. Having said that it has just occurred to me, they called him two days afterwards. That doesn't mean anything does it?
you may as well let a Chimpanzee connect the system up then, lets face it, he has connected it up wrong, end of LOL
 
ok...its a zone valve yes....
so its s plan...
first check the salamander box...

you should have a supply..phase, neutral & CPC

from that you will have the supply going into the control....
it will be linked out in the back of that....3 and 5...i think...
you will have then a twin coming back out from the control wallplate and into the salamander box.....one core of this will go to the room stat....the other to the cylinder stat....then from there back to the salamander box and to the zone valves...
the zone valves require a neutral & CPC + a perminant live from the incoming twin....(use the grey for this)....the orange then goes to the boiler & pump
 
Last edited:
Firstly preparation - understand the system you are looking at, find out what kind of plan it is and download the wiring set-up for this system - then go to check it is wired as it should be, how do you expect to be competent in fault finding in a system you haven't checked that it is initially connected up correctly ..... the system should have been fully tested to operate in all states before you left the last time if you lack the plumbing knowledge to understand the way the system functions you liaise with the plumber till you can understand the sequence of operation when calling for hot water or heating. You can isolate section while powered down and eliminate them as possible faults, whith the plumbers input try manually switching the valve testing as you go ... be careful with insulation tester when electronics are connected like the clock or boiler...... i am in my job forced to test my machine faults without wiring plans or instructions as the equipment is usually 50-70 yrs old without off the shelf part replacement but given the chance if available i always familiarise myself with the schematics and liaise with the operator to identify possible likely areas at fault..... half the time its mechanical issues or operator error and the electrics work fine ...... this is the worst thing trying to find a fault that doesn't exist because the operator has left the gearing in the wrong set-up.
 
Darkwood,

Basically, due to the two wiring centres, it is a mess. I was hoping to avoid them! I was hoping the more experienced on here would say "there is a common fault with stats caused by ...." thus saving me hours going through the two different wiring centres at different ends of the house figuring out the mess someone else has installed.
 
RmBo_O

That is sort of the conclusion I have already come too. To be honest, I don't mind the work, it's just the hassle trying to get money out of people for several hours work re-wiring something "...but it used to work fine". But that's a conversation for another day and another thread....
 
Given that the system has operated for various periods......should/could any combination of parts draw significantly more than 3 amps. Is the pump sticking?
 
Considering that the stat is purely a switch (most are even class 2), it's unlikely that this can be the problem. I would definitely be disconnecting the electronics and IR testing the circuits.
Also worth checking that the 3A SFCU isn't also supplying something else :)
 
If the plumber wired it up then the plumber should be localising his own faults. If not give him a reasonable hourly rate and reinstall the thing to a standard where it can be easily worked on then go about finding the fault assuming you don't discover it during the reinstall.
 
trying to sort out a c/heating problem on a website is pure stupidity
the o/p shouldn,t tackle the job if he knows f/all about c/h wiring and shouldn,t charge any money as he,s out of his depth
he should tell the customer that he know sweet f/a, and recommend someone who does
 
It's been quite warm recently so I bet everything has been ok when either the hot water or ch has been on independently, but when both on there is a problem, time to delve into the wiring centres and trace everything through, I had a similar problem, my plumber friend did a load if work to a system and when he finished it isn't work, although it all worked before he started, I traced it to the pump not working correctly, but he would t have it that that was the problem, moral of story always check everything yourself and don't listen to plumbers who play with electrics
 

Reply to cyclinder stat blowing fuse in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
630
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
977
So a customer changed his own stat and wired it wrong and blew 3/4 fuses. Then heating was stuck on so I changed the programmer and this resolved...
Replies
10
Views
1K
I recently wired a heating system with a UFH8 manifold and an unvented cylinder.... easy. Well it threw up a few problems. Initially I had the...
Replies
3
Views
3K
Hi guys, Do you know if I can install a Nest E with the heat link in the airing cupboard as opposed to the room stat position? System is a S plan...
Replies
1
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock