Search for tools and product advice,

Discuss DB installed connected & tested in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
Just your thoughts on this DB,it’s a Lewden type,I personally don’t like them.
Bus bar,not ideal,main switch on right,space very tight to make connections,hate the rcbo’s,screws in front of each other,making it hard to retighten .

CF836C78-E307-4486-AB06-4B3FEEBF529A.jpeg
 
@Leesparkykent its a time delayed one so "should" be ok, you can just see the S on the front of it.... The rcbos are only single pole though so there still isnt perfect discrimination and a fault remaining on the neutral will trip the whole supply... Not a great setup imo...
 
@Leesparkykent its a time delayed one so "should" be ok, you can just see the S on the front of it.... The rcbos are only single pole though so there still isnt perfect discrimination and a fault remaining on the neutral will trip the whole supply... Not a great setup imo...
Yes that was exactly my point. Neutral earth fault and the RCBO will trip but the upfront RCD, time delayed or not will still trip as the RCBO's don't break the neutral.
 
Yea,the problem is that the 63 amp breaker supplies a Loxone lighting panel,Rcbos in that Panel serves lighting .
So that was the purpose for the 100 ma td Rcd,discrimination for the other rcbos.
 
I thought it was time delayed ? How will this meet disconnection times ?
Bear with me as I have nothing to do with TT systems and probably lack a lot of knowledge in this area.
Hi - TT disconnection times for a distribution circuit is up to 1 second from Reg 411.3.2.4 :)
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

491382E2-7CEE-4D2D-B27D-441EBF1028E6.jpeg
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.
Trouble is unless they are double pole rcbos then you have provided no discrimination.....
yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.
 
But N/E faults are mighty common? Meaning that one ANYWHERE on that install will cause the upfront to trip loosing the entire installation.

imo that doesnt comply with the regs so either DP rcbos or an alternative design should have been considered.

Also imo on TT with a full rcbo board the 100ma S is not required upfront so youd actually be better off swapping that mcb for an rcbo and the upfronter to a main switch...
 
Last edited:
Ok,but then neutral to earth faults will not be disconnected at all,they will remain,unless DP rcbo’s are used.
The reasoning for the time delay is,discrimination for the lighting panel,which have its own rcbo’s.
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

Not double pole but switched neutral. These would of done the job.
Wylex NHXS1B32 32 Amp 30ma Type B 1 Module RCBO - Edwardes - https://www.edwardes.co.uk/en/products/wylex-nhxs1b32-32-amp-30ma-type-b-single-pole-1-module-rcbo-?utm_medium=google_shopping&utm_source=google&utm_campaign=google_shopping&gclid=EAIaIQobChMIxemvxrWc2wIVypPtCh23egO4EAQYASABEgLWBfD_BwE
 
This came with the rcb’os,providing a upfront Rcd is used,it’s ok-ish,I realise discriminating may not be ideal,but what else can you do,on a TT system.

yea,your talking about the N/E faults that may happen,discrimination will occur when there’s a L/E fault.
Who on earth uses double pole rcbo’s,.

I do, TT quite common around here so I use an SBS board.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
You are literally talking milli seconds before the upfront RCD trips aswell as the RCBO. what's the installation method of the distribution circuit feeding the loxone?
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
 
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
Yea I can see where everyone is coming from,we are talking about a n/e fault here,I know it’s on aTT system,but realistically
These faults may be happening all the time,on most earthing systems,with negligible currents flowing.
N/e faults have always been a pain,& so be it if all power is disconnected,also if the rcbo disconnects that circuit surely that prevents any fault being on that circuit ie:N/E.,no current will flow to Earth ,arguing the fact the rcbo will trip on a N/E fault.
This is getting mighty confusing.
 

Reply to DB installed connected & tested in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
4K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock