Discuss Delay time S type RCD or not RCD in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
24
Hi guys,

Got job ...studio flat just done some odds and ends that requires i put new RCD CU in property.
Very small load currently being fed by T&E from OLD wylex MCB in cupboard on ground floor. Question is The cable of which i did not install
is run (from what i can see) under floor boards into riser under more floor boards, to the CU in studio (CU in studio is about 6" from floor in cupboard.
Opinions on whether a RCD S type should be in place to protect sub main cable. only part of T&E exposed is under the stairs which is an electrical cupboard. rest under floor etc.....

????????
 
you only need RCD protection on your feed if that feed is buried <50mm in a wall without earthed protection. if it was you'd have to fit a 30mA RCD anyway.
 
What though if this cable is running <50mm from underneath of floor boards as many a hole has been drilled or cut....
obviously not buried but nails through floors etc etc......would that be situation whether discernment might be required. I mean i have no idea of finding that out but as im dealing with that circuit would i be responsible? Or as its just New CU in studio flat am i not responsible for the condition and arrangements of supply feed? thought i would be


 
BS7671 specifically says cables buried in walls. (522.6.101). no mention of floors.
 

Reply to Delay time S type RCD or not RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
553
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock