Discuss Domestic Ze ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Peter Woodford

Guys,

just thinking, how sad on a sunday morning. If you had a consumer unit in a garage ran from the main board in the house would you do the Ze tests in the house ( i am thinking yes unless you had a earth spike near the garage is this right). Also if you did put in a earth spike at the garage i take it would also bring your zs readings down from the circuits that come off that board in the garage

can someone confirm thanks
 
Ze is always measured at the origin of the installation.

What you would measure at the garage DB would be the Zs and PFC of the sub-main supplying it.

As for an extra spike in the garage this would depend on wether you had a TT, TN-S or TN-C-S earthing system to start with. If not a TT then probably no bearing at all as the resistance would probably be too high to make a difference to the readings compared to the TN-S, TN-C-S and bonding conductors etc.
 

Reply to Domestic Ze ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
443
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
888

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock