Noticed this on the architects notes can someone elaborate for me? thanks

the contractor should note the need for dual earth terminal blocks to be provided within DBs supplying computer power
 
IT equipment have high earth leakage currents so need 'High Integrity Earthing', the cpc should be connected to separate terminals on each socket on such a circuit and if it's a radial circuit a cpc should be taken from the last socket back to the DB.
Have a read of this...
http://electrical.------.org/wiring-matters/26/5437-earthing.cfm?type=pdf
 
I believe the type of earthing circuit depends on how high the total earth leakage current from the computers is.I am doing two rows of 4 and one of 2 at the moment,radials and each row has its own RCD.I will check the leakage current but I expect it to be very low.
 
if you ain't come across it before, you won't know. i know a few sparks who are " old school" had never heard of high integrity earthing till recently.

Well they should have because it is not "that" new, if they want to be classed as professionals then they must act as such.
Sorry my opinion stands, if the OP does not know then back off and get someone who does.
 
Well they should have because it is not "that" new, if they want to be classed as professionals then they must act as such.
Sorry my opinion stands, if the OP does not know then back off and get someone who does.
I thought the idea of this forum was to gain advice for things you are not sure about....the rudeness of some posters on here is breathtaking...........
 
I've just done a PIR on a large home office that had 10 PCs in and on day of test there was 27mA of earth leakage on the dedicated RCD circuit for those PCs (therefore approx 3mA per PC). Client reported occasional trips. Solution is another RCD as above. Thank heavens for the ramp test!
 
I thought the idea of this forum was to gain advice for things you are not sure about....the rudeness of some posters on here is breathtaking...........


I did my apprenticeship in the sixties in maintenance and at the time "I knew it all"or so I thought
icon7.png
icon13.png


I found during my career,mainly installation, that others knew things I had no idea of
icon9.png

Conversely,they were blind to subjects I thought were fairly routine
icon14.png
icon7.png

You see where this is going to
icon12.png
icon4.png


The only thing I will say is this,
Electrical work is a vast area, and one that luckily is covered by someone or other on this forum
icon14.png


Reciprocating your knowledge is what the forum has been, and I hope will continue to be
Some give of their knowledge freely.others not so perhaps,but where would the forum be, without all of us lacking something or other to acquire
 
I did my apprenticeship in the sixties in maintenance and at the time "I knew it all"or so I thought
icon7.png
icon13.png


I found during my career,mainly installation, that others knew things I had no idea of
icon9.png

Conversely,they were blind to subjects I thought were fairly routine
icon14.png
icon7.png

You see where this is going to
icon12.png
icon4.png


The only thing I will say is this,
Electrical work is a vast area, and one that luckily is covered by someone or other on this forum
icon14.png


Reciprocating your knowledge is what the forum has been, and I hope will continue to be
Some give of their knowledge freely.others not so perhaps,but where would the forum be, without all of us lacking something or other to acquire
THATS THE SPIRIT DES!....Most posters on here are out to offer advice and guidance whilst gaining some themselves. I look at it like this...if it wasn`t for institutions like this forum you`d end up with loads of installs "going wrong" at some point or another: We need someware to share advice and have a laugh whilst doing so...we`d all go mad if we didn`t..lol..:grinningelf:
 
Stick me in front of large motor control gear and I'd have to go into BS mode and I don't mean 7671!

Stick me in front of a modern CU and I look confused, give me the MCC anytime. Don’t get me wrong I’d soon suss it out but it’s foreign territory to me!

Until I came on to this board I didn’t even know a MCBO existed.
 
Well they should have because it is not "that" new, if they want to be classed as professionals then they must act as such.
Sorry my opinion stands, if the OP does not know then back off and get someone who does.

In which case dont bother replying to the thread - your comments are neither useful or wanted
 
i did 16th in 1995 and no mention was made of hi integrity earthing then. it was only in 1998 when working in factory offices that i came across it, and that was after 25 years in the trade. as i said before, if you ain't met it, you don't know.
 

Reply to Dual earth terminals for computer circuits in the Australia area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, I've been getting into electrical work these last few months, and have gone from doing rudimentary battery-switch-bulb diagrams to...
Replies
1
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock