Discuss EDF meter change fault in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Hello guys

EDF came out to a flat and attempted to replace the meter.

I have been called out to investigate there comments which are “unsafe to remove meter, possible borrowed neutral, voltage at meter even with fuse removed (dropped neutral test)”

First off i am currently on site, I removed the fuse and tested potential between N in and N out no voltage.

I then tested all live conductors to earth and no voltage.

Question is what is this dropped neutral test and and I missing something with my testing as I can’t see a problem?
 
I think they have used the wrong phrase when they say borrowed neutral. As above it sounds like a DNO issue rather than a borrowed neutral on the consumer side.
 
i done an impedance test between the L-N at the meter and got 0.08 ohms so I don’t even think it’s a broken PME or neutral if that what they meant.
The meter man said to the client with the fuse pulled out he was getting voltage on the neutral.
Unless he has an different means of testing there is no voltage between N in and N out at the meter or between and earth or live.
Not sure what else I am missing
 
report attached from EDF meter man
 

Attachments

  • 869D4431-D89D-4BB8-8F88-B93A0A4C536C.png
    2.8 MB · Views: 43
Does he mean he gets a voltage on the neutral on the supply side of the fuse carrier or the consumer side?
 
a) So the implication is the neutral (and TNC ) Earth will rise up to Line potential as a load is placed L to N ? ( Depending on additional earthing / Bonding ) Not nice !
Or is it TN-S.
b) Not DNO side
( Or are they witnessing lots of Line leakage into wall , confusing "their volt sticks -perspective on things .. Hope not)
c) Power sneaking into install from leakage - Neigbours outside lights
(More added since Liked..!)
 
Last edited:
It may be a Neutral from another flat (or shop?) within the building.
Are you testing with the C.U OFF, try with all MCB /RCBO ON and C.U mainswitch ON.
Meter person should have had the CU off before pulling the fuse, maybe they didn't.

What about Reverse Polarity at the cutout?
 
Last edited:

Reply to EDF meter change fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
486
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
903
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
840
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock