Discuss EICR - How much do you check? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
I have been to 2 different rental properties this week, one for an EICR and the other for a report of the smell of fish from the shower isolator when the shower was in use.

As part of the EICR, I removed the shower cover to measure R1+R2 and Zs at the shower and a general inspection, only to discover a loose connection and a badly damaged terminal block in the shower which had overheated. Also at the same property in same shower, a loose connection had melted the back of the isolation pull cord so the isolator was stuck permanently on. Both rectified and put back into service.

At the fish smelling isolator, it was a wall mounted 45A DP isolator with neon outside the bathroom. Same again, loose connection, melting the cable insulation and back of the switch.

Being rental properties I hoped to get hold of the previous EICR's but I had no access to them for one reason or another, but I did wonder if anyone had ever checked these items before. In both cases the cables were so loose in their connectors I question whether they had ever been tightened and also whether they had ever been checked.

Loose connection overheat.jpg


IMG_0463.jpg
 
Its usually a progressive exercise,find problems and look deeper for more
Having said that,shower circuit connections are notorious for being poor and they need inspecting as routine.


Looking at the effort that was made in those pictures,I would be on my best rip the installation to bits behaviour
 
A couple of strands missing out of the neutral as well.
 
Its usually a progressive exercise,find problems and look deeper for more
Having said that,shower circuit connections are notorious for being poor and they need inspecting as routine.


Looking at the effort that was made in those pictures,I would be on my best rip the installation to bits behaviour
I did - It wasn't hard though, most of it was staring me in the face without digging deep. It's a real mess.
 
don't let IET see those pics. the 18th will have an amendment within 12 months , calling for all showers to be housed in non-combustible enclosures.

Lol I'm imagining a galvanised cubicle with wired glass door. Swmbo would have a fit. Could always fit a sprinkler as well, just to be on the safe side. Maybe the sprinkler could then be used as the shower. Hang on ! It's a "there's a hole in my bucket" moment.
 
don't let IET see those pics. the 18th will have an amendment within 12 months , calling for all showers to be housed in non-combustible enclosures.
Just noticed the implications of your post Tel very clever indeed.
 

Reply to EICR - How much do you check? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs...
Replies
10
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock