Discuss EICR on marina helpppppp in the UK Electrical Forum area at ElectriciansForums.net

Are you carrying out an EICR or are you looking at a Report done by someone else.
Sorry but I'm still struggling to understand the question. There will be a Ze at the intake, and a Zdb at each sub board. The maximum permitted Zs at each DB will depend on the OCPD protecting the distribution circuit.
Yes I’ve got Zdb and ka, but I’m on about max Zs left hand side of RCD X1

A7468C60-1C94-4214-9A7E-158206E97671.jpeg
 
What is circuit 1TP?.....whatever it is, you want the measured Zs for it.
Not much more testing carried out...IR, for starters.
 
It can't be far away, judging from the Zdb and Zs.
and if it's 3 phase, it's badly put together.
edit. Gone....you can but try.
 
It's not a final circuit then, it's a distribution circuit, and the schedule is specific for the distribution circuit. The final circuits will be connected to whatever DB it feeds, and there will be another schedule for those.
 
It's not a final circuit then, it's a distribution circuit, and the schedule is specific for the distribution circuit. The final circuits will be connected to whatever DB it feeds, and there will be another schedule for those.

If you’ve been reading I’ve put I’m an apprentice and I’m working with people just like to ask on here instead of looking stupid at work but thanks for your help
 

Reply to EICR on marina helpppppp in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock