So just put NA just confused as who ever did it last put a reading downIt's not a final circuit then, it's a distribution circuit.
Discuss EICR on marina helpppppp in the UK Electrical Forum area at ElectriciansForums.net
So just put NA just confused as who ever did it last put a reading downIt's not a final circuit then, it's a distribution circuit.
It's not a final circuit then, it's a distribution circuit, and the schedule is specific for the distribution circuit. The final circuits will be connected to whatever DB it feeds, and there will be another schedule for those.
If you’ve been reading I’ve put I’m an apprentice and I’m working with people just like to ask on here instead of looking stupid at work but thanks for your helpIt's
Sorry to get this right, DB1 feeds DB2 taken readings at DB2 Zs reading at DB2 will be recorded on DB1 as Zs for distribution circuit and DB2 Zdb will be same readingThe Zs for the distribution circuit will be the same as Zdb at the board it is feeding.
Sorry to get this right, DB1 feeds DB2 taken readings at DB2 Zs reading at DB2 will be recorded on DB1 as Zs for distribution circuit and DB2 Zdb will be same reading
On the water hahahahaAs a matter of interest where is this marina.