EICR on a marina, say I have a distribution unit with 3 BS88 fuses each one feeds another DU A,B,C for instance say for DU B I have circuit details then schedule of test results for the main DU that feeds the others but on that one it says Max Zs reading for DU B theres no dead testing so, then another circuit details and shedule of test results for DU B it’s self with sub circuits which I will put Zs as my highest from testing all sockets will my max Zs just be my Maximum Zsb from testing DU B itself? For my main DU reading for DU B
Hope it makes sense
 
EICR on a marina, say I have a distribution unit with 3 BS88 fuses, each one feeds another DU A,B,C, for instance.
Say for DU B I have circuit details, and a schedule of test results for the main DU that feeds the others, but on that one it says, max Zs reading for DU B there's no dead testing, so, then another circuit details and shedule of test results for DU B it’s self with sub circuits which I will put Zs as my highest from testing all sockets will my max Zs just be my Maximum Zsb from testing DU B itself? For my main DU reading for DU B
Hope it makes sense
 
He is getting his hand - held instructions on the screwfux forum (God help him). Seems he's not aware that for a downstream DB (Its a marina) the Ze can be n/a.
 
Last edited:
Confusing hahahaha I’m only an apprentice so still trying to learn, there’s a Main DB which feeds another DB say DB1 which has a main switch that feeds a another DB say DB2, there’s a shedule of circuit details and results for DB1 to DB2 which I’ve measured the Zsb and ka at each one but confused will my Maximum earth loop impedance be the same as Zsb as it’s only the sub cable feeding the DB2 as no dead testing involved
 
Confusing hahahaha I’m only an apprentice so still trying to learn, there’s a Main DB which feeds another DB say DB1 which has a main switch that feeds a another DB say DB2, there’s a shedule of circuit details and results for DB1 to DB2 which I’ve measured the Zsb and ka at each one but confused will my Maximum earth loop impedance be the same as Zsb as it’s only the sub cable feeding the DB2 as no dead testing involved
Sorry but I'm still struggling to understand the question. There will be a Ze at the intake, and a Zdb at each sub board. The maximum permitted Zs at each DB will depend on the OCPD protecting the distribution circuit.
 
Didn’t realise you could do an EICR on a marina....
9585E41D-2CDE-42C1-98FB-6725FA9D5239.jpeg
 

Reply to EICR on marina helpppppp in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock