Discuss electric shower tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Been asked to find out why a new shower is tripping a new cu rcd,
new shower 9.8kw mira
supplied with 10mm T&E
40amp mcb protected by 63a RCD
Its a new cable thats been run in and I have no equipment to test the continuity etc I went right back to basics ,missed out the 45amp DP switch and it still tripped,then wired it straight into the DP isolator switch of the cu and the shower started straight away I should also say that this cu is fed from the main house but the shower did not trip the main cu.
The mira instructions say to fit a 30a rcd

Anyone any ideas ?

Ta
 
Thanks for the reply as I said I have no proper testing equipment I have a fluke ,continuity was fine with this,and yes you are right it is 30ma ....really should proof read posts I'll check the neutral is in the correct bar next time I'm out..
 
ok got that, would this occur even if the cu is split load ?
and if there is an N-E fault elsewhere why is this not tripping the rcd

things were much easier in the 70's sparky wise....a meggar for testing and a wire coat hanger and a piece of string with a plug chain for fishing cables...
 
A 41A load on a 40A ocpd is not a good start!
Without test equipment you are going to waste a lot of time and effort.

If I've read the op correctly, which I hope I haven't, you have bypassed the protective devices by connecting the circuit directly to the main switch of the CU?
 
Think you've read it right Dave, if not we both need to learn to read. That's how I read it as well.

I don't really understand going to look for a fault without test equipment either, maybe I'm getting too old for this.
 
Really should take more notice but I was more concerned theat the rcd was tripping and didnt (or cant )remember if both had tripped I have a feeling the the mcb is 40a as it was one of those pre-populated CU's that he bought
and Ive just done a quick calc for a 9.8kw appliance and its 40.833333333a...
 
In reply to the above ,I'm doing a pal a favour in trying to find the fault, the original installer is not returning his calls
I think some of the problems have arisen due to my pal buying the materials himself to save money.
and ..FYI I don't have any test equipment as I've been effectively off the tools since 1986..save for the odd light fitting and extra socket
 
yes I agree but we didnt have all the all singing and dancing equipment in the late seventies /early eighties it was a case of disconnecting everything and starting from the cu ....
we only had one megger between two of us when on the tools, I completed a pyro installation and the only way I could bell out the cores was to connect to to the supply and hope that the cores had sealed properly and the pot was on straight...
 
You don't need anything all seeing & dancing just an Insulation tester & maybe a Clamp meter to check Earth leakage.
If the installer left it like that though, you have to wonder what else you might find.
 
Been asked to find out why a new shower is tripping a new cu rcd,
new shower 9.8kw mira
supplied with 10mm T&E
40amp mcb protected by 63a RCD
Its a new cable thats been run in and I have no equipment to test the continuity etc I went right back to basics ,missed out the 45amp DP switch and it still tripped,then wired it straight into the DP isolator switch of the cu and the shower started straight away I should also say that this cu is fed from the main house but the shower did not trip the main cu.
The mira instructions say to fit a 30a rcd

Anyone any ideas ?

Ta
Well wiring it into the CU M/S and it wont trip, cus there is nothing to trip
 
I dont have a megger, I have a fluke, Installation practices of 40 odd years ago are still practiced today,its the way they are installed ie bad workmanship that cause the problems,wiring systems have not changed since I was on the tools but certain regs have,earthing,testing,circuit discrimination I could go on but ultimately most of it is down to bad practice.
I would have had my a**e booted from my journeyman for some of the installations I have seen
 

Reply to electric shower tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock