I dont think the maths is the same.

When PME and using a supplementary earth rod it takes into account the max current of the installation and this is put into the equation which brings up a low Ra value.[/QUOTE]
 
When put into maths it requires a stupid low Ra value which cannot in reality be sustained.

That's my understanding?
Yes we did some calcs at college when we did the course. It was nigh on impossible. I think 3 earth rods 1 meter apart 2.4 meters deep might do it. Depending on resistivity of the earth.
So they have given us a solution to the problem that is pretty pointless.
 
I dont think the maths is the same.

When PME and using a supplementary earth rod it takes into account the max current of the installation and this is put into the equation which brings up a low Ra value.
[/QUOTE]
You don’t take the pme into account when doing the maths as the rods are there in case you loose the neutral, thus loose the pme.
 
The major point of TT for ev is in case of dropped neutral on supplier side.

That in itself is pretty rubbish that we have to prepare for faults that are nothing to do with our regs and are in the control of the DNO’s.

So we need to know that the earth rods being put in at the origin are adequate without the pme if the neutral is lost by DNO
 
These are not my suggestions, they are what I was taught on the City & Guilds course in EV charging that I did. I dare say that anyone else who has completed the course would have been taught the same.

If these 'suggestions' amuse you, why not e-mail Bill Allan of NAPIT and laugh loudly at him while you tell him that you know more about EV charging than he does. Meanwhile, kindly desist from trying to me appear foolish. Fair enough?

https://professional-electrician.com/18th-edition/changes-introduce-shock-risk

I don't claim to know more about EV charging than anyone. However is is obvious (hopefully) that introducing an extraneous earth potential into an installation then connecting it to a big piece of exposed metal (car) goes against the basic principles of protection against electric shock.

I am not trying to make you appear foolish, I have no need to do this. By suggesting that one can laugh loudly in an email you have achieved this appearance without my input.
 
if the prohibition of PME for EV chargers is to eliminate risk if the supply N is lost (as with metalclad caravans) the I can't see any reason to differentiate between inside or outside. a fault occuring would have a similar result, in or out. then, i have not done any research on EV so my knowledge is limited.

If the vehicle is inside then it is, technically, within the equipotential zone and becomes no different to any other exposed, earthed, metal in the building. The car being charged in the garage presents the same hazard as the class 1 freezer in the garage.
 
New posts

Reply to EV Charger Installation - Cabling Query? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
4K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
610
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock