Discuss Extraneous Parts Earth sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
13
Customer wants to take power from an existing garage (with board) to supply a greenhouse, to be fitted with ip rated switchgear.
The greenhouse is made of aluminium.

Since this is an extraneous conductive part am i right in thinking that the aluminium frame would require a 10mm bond at least? (tncs supply)

Garage is fed with a 4mm armour (3core)

Should i still take the supply from the garage but run in a seperate 10mm earth from the house MET?
 
What's being put in the greenhouse? Maybe an IP rated outlet just outside it would allow use of garden tools etc.
 
would you like to elaborate on what yous are talking about?

you've mentioned this concrete plinth idea. (which ive never heard of)
Why would an extraneous conductive part not need earthed if sited on a concrete plinth? Wheres the logic?
Because,combined with the human body,a res of 23k would only allow a current of 10ma to flow which is considered safe.
 
Right that makes perfect sense, thanks.

But, as ive already said, (to much hilarity) the greenhouse is not on a plinth, so why would this apply?
Am i missing something here? (apart from a brain)
Because the concrete plynth may offer more insulation resistance against the path to earth, than if the metal frame was in direct contact to the earth. Just test the frame as already been mentioned if its greater than 25kohms (a safe bet value) then it would not be considered extraneous. But if you find that the tested value is very close to the minimum accepted value (22kohms) and environmental conditions might reduce this value further then its your call.
 

Reply to Extraneous Parts Earth sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock