Discuss Extraneous Parts Earth sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

so what about, i take the tncs supply from the garage (2.5mm 3 core armour). This would supply earth to all of the circuits only. And then seperatley i connect a 10mm earth onto the greenhouse frame and then into a earth rod?
 
No good I'm afraid.
By earthing the frame with a local rod you ensure it is an extraneous conductive part and so needs connection back to main earth terminal. Or TT'ing. See @davesparks post #19 :) .
 
basically im trying to get out of digging a trench back to the house (many reasons).

But my other problem is that inexperienced with "tt ing" something.
So im just supposed to run a live neutral from the garage (unearthed) to the greenhouse, then stick a 30ma board/earth rod.

or do i earth the armour at the garage side but leave the greenhouse side unconnected to its respective earth terminal.
 
or do i earth the armour at the garage side but leave the greenhouse side unconnected to its respective earth terminal.

yes. earth armoured at supply end. TT the greenhouse. bond the metal frame if required.
 

Reply to Extraneous Parts Earth sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
448
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock