Does this have to be measured at the consumer unit, or can it be done at a socket outlet

Yes as it will be higher at CCU, and the aim of test is to find out what the highest measured value of PFC and then check that protective devices etc are capable of safely disconnecting under fault condition without causing damage to protective devices or conductors.
 
Are you supposed to double pscc? Remember that from college for some reason?

Only if supply is 3 phase and PFC has been measure between each live and neutral, and before some jump on me I heard there are multi tester out there where direct 3 phase measurement can be taken.

Read page 52/53 GN.3
 
Only if it's a 3 phase supply...

Ooops, I was way too slow on answering that one!! But yes, the Megger MFT 15xx will test across 400V.
 
Last edited:

Reply to Fault Current (Prospective) in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, We've had a rewire and our electrican is currently away on holiday so we're unable to ask them for advice. Please can I ask for your...
Replies
11
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
504
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock