Discuss Fitting 16A hardwired oven to 32A cooker circuit in the UK Electrical Forum area at ElectriciansForums.net

assumint]gthe cableis 6.0mm, then you leave it on a 32A MCB as posted previously. although it's a proteus, might not work anyway so a 16A would only make it fail at a lower level.
assumint]gthe cableis 6.0mm, then you leave it on a 32A MCB as posted previously. although it's a proteus, might not work anyway so a 16A would only make it fail at a lower level.
Thanks for the reply - I take it that means I should probably think about a new consumer unit 😂
 
Im going to piggyback this post as im in a slightly same position. I have a 45amp cooker switch with socket on a 6mm t&e to a 32amp breaker with rcd protection. The mrs wants to get the hisense oven and a built in microwave. The oven is 3kw and the microwave is 900watt, the oven says fuse rating 16amps, can i wire the oven to the 45amp cooker outlet and plug the 900wat built in microwave in the same socket on the original setup of 32amp breaker on 6mm t&e on the 45am cooker outlet with sockets
Thanks
 
Im going to piggyback this post as im in a slightly same position. I have a 45amp cooker switch with socket on a 6mm t&e to a 32amp breaker with rcd protection. The mrs wants to get the hisense oven and a built in microwave. The oven is 3kw and the microwave is 900watt, the oven says fuse rating 16amps, can i wire the oven to the 45amp cooker outlet and plug the 900wat built in microwave in the same socket on the original setup of 32amp breaker on 6mm t&e on the 45am cooker outlet with sockets
Thanks
By 'hisense oven and a built in microwave' do you mean the microwave is built into the oven? I doubt it's got 2 separate cables then. Put a 13A plug on it and if you're lucky there'll be an ignition outlet behind there also to plug it into.

If they're separate, your plan has the microwave on a 13A plug in the cooker isolator socket which is fine, and the oven wired straight to the cooker outlet plate which I would do at my house but change it to a fused spur with outlet if you're worried.

A 900w microwave doesn't mean it draws 900w from the supply, I thought it meant 900w 'microwaving power' to the food. Cooking times would be all over the place if all microwaves used 900w supply but all had different efficiencies, and grill functions etc. I'd guess 2kW-2.5kW for a 900w microwave.
 
By 'hisense oven and a built in microwave' do you mean the microwave is built into the oven? I doubt it's got 2 separate cables then. Put a 13A plug on it and if you're lucky there'll be an ignition outlet behind there also to plug it into.

If they're separate, your plan has the microwave on a 13A plug in the cooker isolator socket which is fine, and the oven wired straight to the cooker outlet plate which I would do at my house but change it to a fused spur with outlet if you're worried.

A 900w microwave doesn't mean it draws 900w from the supply, I thought it meant 900w 'microwaving power' to the food. Cooking times would be all over the place if all microwaves used 900w supply but all had different efficiencies, and grill functions etc. I'd guess 2kW-2.5kW for a 900w microwave.
If your microwave is rated at 1000 watts it uses 1 kilowatt (kW) per hour
 

Reply to Fitting 16A hardwired oven to 32A cooker circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735
Hello everyone, I've got a new oven and have a question about installing it. It's a 2.6kW 13A oven, and a cable from the 32A cooker circuit to...
Replies
2
Views
228
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
235
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
219

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock