Discuss Fluorescent fault overcurrent trip? in the UK Electrical Forum area at ElectriciansForums.net

S

SpannerSpark

4ft old style starter/ballast type fitting which when powered does nothing at all (not a flicker) but trips the 6A/30mA RCBO after maybe 3-5 secs. I didnt have my clamp meter with me when i went to see the fault but assume due to the time delay that its the overcurrent part of the RCBO rather than the current leakage part thats making it come out.
The fitting is min 20 years old i would guess, some heating marks on the ballast but other than that the tube looks ok , no blackening. Removing the tube only no trip. Removing the starter only and no trip. Fitted a new starter now RCBO trips immediately. Customer happy to replace whole fitting, but i wouldnt mind knowing what the fault possibly is. Any theories welcome
 
4ft old style starter/ballast type fitting which when powered does nothing at all (not a flicker) but trips the 6A/30mA RCBO after maybe 3-5 secs. I didnt have my clamp meter with me when i went to see the fault but assume due to the time delay that its the overcurrent part of the RCBO rather than the current leakage part thats making it come out.
The fitting is min 20 years old i would guess, some heating marks on the ballast but other than that the tube looks ok , no blackening. Removing the tube only no trip. Removing the starter only and no trip. Fitted a new starter now RCBO trips immediately. Customer happy to replace whole fitting, but i wouldnt mind knowing what the fault possibly is. Any theories welcome
what makes you say this?

could be a neutral-earth fault

whats the earthing arrangements?
 
Ballast partial collapse(high inpedence fault) internally or short depending on what part of the cycle the power is on when the starter opens and recloses could give a delay on a short....
If the tube gives an extra bright flash and refuses to work again the tube elements will have blown out too .

As you have already guessed it sounds like a new fitting or ballast swap.
 
Last edited:
what makes you say this?

could be a neutral-earth fault

whats the earthing arrangements?

A Neutral/Earth fault is highly unlikely as the OP said taking out the starter stops the rcbo tripping this means the only culprit that could cause this (If not a ballast fault) is a short to earth on the wire to the starter from the tube end fed by the ballast and as this has the tube elements in series too and this wouldn't actually be classed as N as the Neutral point ends at the pin on the other end of the lamp.
 
A Neutral/Earth fault is highly unlikely as the OP said taking out the starter stops the rcbo tripping this means the only culprit that could cause this (If not a ballast fault) is a short to earth on the wire to the starter from the tube end fed by the ballast and as this has the tube elements in series too and this wouldn't actually be classed as N as the Neutral point ends at the pin on the other end of the lamp.
yes....
thanks Dark:eek:
 
The delay is most likely due to ballast short as weird as it sounds ...if the ballast can still provide enough field collapse to strike the lamp it should then act as a current limiter (choke) but a internal short will allow overcurrent which will either trip the circuit after a time delay or destroy the lamp as it get warmer the internal resistance falls which is also another reason for delay to occur.

We lack enough info to know exactly what is tripping the mcb/rcbo but i think i covered with this posts most of the possibilities with what he has given us.

Re-reading the OP it doesn't strike so its likely the ballast can't build enough field to give back EMF but still may let overcurrent through and the starter completes the circuit but still will have 2 elements in series (lamp caps).. the starter may well weld with overcurrent stopping the bimetallic strip from opening you get your delay again ... a new starter could open and still send a partial back EMF into the rcbo and trip it until it also welds

I bet the ends glowed with the old starter and not with the new one.
 
Last edited:
How a Fluorescent Light Works - Schematic Animation - YouTube

Watch this Spanner to remind you how the ballast and starter play their role its the easiest one i can find to follow just keep pausing the video as the wording does move by before you can relay it to the diagram.

You'll understand why telling the customer the fitting is knackered is the best way rather than trying to explain to them.
 

Reply to Fluorescent fault overcurrent trip? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’ve got bad ballasts and am replacing the T12 fluorescent bulbs with Halco direct wire, double ended T8 LEDs. The fixture has 4Rapid start bulbs...
Replies
0
Views
600
Hi all, I've been having some issues trying to fix a fluorescent light in the bathroom. Here's the steps I've taken so far after it suddenly...
Replies
8
Views
1K
I have a bathroom mirror with 2 x 21W fluorescent T5 tubes and an IR sensor. The tubes switch off after a few minutes. I have changed the tubes...
Replies
18
Views
3K
Actually managed to kill 2 PIRs in succession yesterday. The first I got SL and N mixed up (who uses the black core of a 3C+E as neutral...
Replies
12
Views
2K
Hi I don’t know how resolve this so any helpful advice would be greatly appreciated. I have no electrical knowledge. I will try to be as clear...
Replies
57
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock