a few factors would decide if I would recommend replacement .........
Is the backboard or frame of any of the 3036's made of a combustible material
How do the retro MCB's fit and interface with the existing board and do the cause any exposed parts
How does the cover fit and the subsequent fuse cover fit with these in place, as if both don't fit then this contravenes manufactures instructions
Is there any sign of over heating on with the carriers, busbar or blades
Is the existing installation suitable for the loads and the size of cables and total demand
The possible lack of a single point of isolation
The reason for the test and the expectations of the client, ( some of the tests I do are required to have a clean sheet)
Measured Zs readings and their relation to the fitted protective devices and their disconnection times
The earthing arrangements, this is a Tn system but a TT would require replacement.
That's just a few to start and is not ment to be exhaustive as I'm walking round morrisons ATM lol