Discuss Garage cable mounting in the DIY Electrical Advice area at ElectriciansForums.net

T

tom6

Hi All,

Looking for some confirmation / advice.

I have recently built a garage and will be getting it wired shortly, it is of timber frame construction and timber cladding outside and will have kingspan insulation with plasterboard finish inside with all joints taped and plastered.

Is it ok for all cables to be mounted behind the kingspan insulation obviously supported with clips where required. All the cabling will be ran in the loft and just dropped down the wall for sockets & light switches

Many thanks
 
you'd need to derate your cables by 50%. eg. 2.5mm will be down to 13A. personally, i'd do the drops surface in mini-trunking or pvc conduit and use surface boxes.
 
Perfect thanks for the clarification, will go with the PVC conduit drops.
 
i would use the shatterproof boxes with 20mm knockouts, and with adaptors on the conduit. makes a neat job.
 
If this is going to be a bog standard garage, that only needs power for a bit of lighting and the odd power tool on occasions is the derating really going to be an issue?? Could even use 4mm radial(s) if you're that worried.

Trouble with surface work in a domestic garage, is that it collects dust and debris and ends up looking tired over time. Seeing as you're going to the lengths of boarding this garage out, think i'd prefer to see flushed outlets and switches.
 
Seeing as you're going to the lengths of boarding this garage out, think i'd prefer to see flushed outlets and switches.

I did a six car garage on a newbuild a while back that had something like a dozen flush sockets, walls plastered, log burner, loft insulated... it was every bit as good and the same size as a bungalow!!
 
I've moved this to the DIY forum for you Tom.

I'd also add that certain types of styrofoam/polystyrene insulation can cause PVC cable sheath to deteriorate quite rapidly so conduit or trunking may be necessary where contact may occur.
 

Reply to Garage cable mounting in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
213
I'm in the process of installing Catenary Cables to support 2x SWA and 2x cat5e cables, over a distance of a small distance of 1.5m. The cable...
Replies
2
Views
1K
Hi All, Wondering if I can get some advice. Basically I’m having exposed joist ceilings in my house and I’m in the process of slowly changing all...
Replies
5
Views
1K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock