Discuss Get a shock when you touch sink and oven at same time?? in the UK Electrical Forum area at ElectriciansForums.net

I understand this could be because there is no bonding, but just want to know how it’s possible for the pipework/sink to become live?? Is it through a fault on another circuit finding it’s way to the pipework?
Other way round.

There is probably a fault on the oven that is not earthing via the oven circuit earth.

When you touch the sink, you and the water pipework are providing the earth path.

Get it looked at pronto.
 
Last edited by a moderator:
I would also isolate the power to the oven by switching the breaker off / removing the fuse in the consumer unit / fuse box, until an electrican has been to check out the fault
True, but it might still happen if the MET is not connected and the oven-sink touch is the only place leakage gets to flow.

Not something to use your body to check!!!

As you say, this needs professional investigation ASAP.
 
whilst awaiting the sparks' visit. you do the cooking. get 'er indoors to do the washing up. but don't hug at the same time. ?
 
Other way round.

There is probably a fault on the oven that is not earthing via the oven circuit earth.

When you touch the sink, you and the water pipework are providing the earth path.

Get it looked at pronto.
Which mod edited my gibberish and Why?

Thanks and all, just like to know where I went wrong.
 
I understand this could be because there is no bonding, but just want to know how it’s possible for the pipework/sink to become live?? Is it through a fault on another circuit finding it’s way to the pipework?
Take notice on what other chaps are saying ! this is seriously dangrous turn the oven off till you get it checked theres potential for serious injury or death here.
 

Reply to Get a shock when you touch sink and oven at same time?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
431
I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
Replies
46
Views
4K
I have an electric oven - now many years old. I have replaced the main circular 2.5kW oven element (ELEHY6708) several times over the years...
Replies
9
Views
1K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock