just been looking through an EICR we've had done and there's x4 circuits on D type mcbs which have been given c2's as the zs is higher than the maximum permitted......
Iv looked c type would bring this within the maximum permitted
I don't see why these need to be on D's
2.5 t and e on 20a dtype
Woud this be as simple as swapping the mcbs for c's
One of the circuits is 1.5mm so I'd be lowering this to a 10a !
Iv looked c type would bring this within the maximum permitted
I don't see why these need to be on D's
2.5 t and e on 20a dtype
Woud this be as simple as swapping the mcbs for c's
One of the circuits is 1.5mm so I'd be lowering this to a 10a !