Discuss High zs on low bay lighting circuits in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
174
just been looking through an EICR we've had done and there's x4 circuits on D type mcbs which have been given c2's as the zs is higher than the maximum permitted......

Iv looked c type would bring this within the maximum permitted

I don't see why these need to be on D's

2.5 t and e on 20a dtype

Woud this be as simple as swapping the mcbs for c's

One of the circuits is 1.5mm so I'd be lowering this to a 10a !
 
Last edited:
How many and what type of lamp?. It may be worth a call to the MCB manufacturer if a table is not in their technical information. I thought that lighting circuits were only allowed up to 16A.
 
How many lights are on each circuit? I'm assuming this is Discharge Lighting? Been a while since I looked at the regs but it's something like 1.8x normal load to alow for discharge lighting isn't it? They may have just been trying to cover themselves by sticking a D type on so it doesn't trip on start up. You could probably get a rough idea of startup by adding all the lighting loads and working it out but like westward10 said it might just be easier to suck it and see.
 
How many lights are on each circuit? I'm assuming this is Discharge Lighting? Been a while since I looked at the regs but it's something like 1.8x normal load to alow for discharge lighting isn't it? They may have just been trying to cover themselves by sticking a D type on so it doesn't trip on start up. You could probably get a rough idea of startup by adding all the lighting loads and working it out but like westward10 said it might just be easier to suck it and see.
I'm guessing there going to be either 250w or 400w metal halide
 
I've never come across any lighting circuit protected by a D type mcb before, sounds like poor design if too many lights on start up actually requires the mcb to be D type.
 
Very limited EICR n/a in points served

TBH I don't think it's been done very well 5 3phase boards in the day
Feel for you mate, had a look at one a few days ago and they stated 'Not enough RCD protection' on a site with 5-6 large three phase boards...no more specific than that. They also thought a missing 'Mixed Colour Warning Label' was classed as C2 as well.
 
Feel for you mate, had a look at one a few days ago and they stated 'Not enough RCD protection' on a site with 5-6 large three phase boards...no more specific than that. They also thought a missing 'Mixed Colour Warning Label' was classed as C2 as well.
I don't understand how they have got a zs for every circuit ,going to be a nightmare this one hahah
 
I've never come across any lighting circuit protected by a D type mcb before, sounds like poor design if too many lights on start up actually requires the mcb to be D type.
See plenty of type 4 and D on this type of lighting.
 
And that's why type D aren't the best idea when type C is available.
Isn't a C type 0.87? I might be wrong I've just done it on my calculator rather that check the regs. But it would mean a C type wouldn't work for one of them results. Could always drop to a 16A type c maybe if they are 2.5mm's...that'll give you 1.09. D types are awful, avoid like the plague. All depends on the load you have on the circuit really, shame they didn't record it.
 
Other options for high zs would be rcbos tho may have problems with nuisance tripping or localised supplementary bonding of the lighting circuits
 
Isn't a C type 0.87? I might be wrong I've just done it on my calculator rather that check the regs. But it would mean a C type wouldn't work for one of them results. Could always drop to a 16A type c maybe if they are 2.5mm's...that'll give you 1.09. D types are awful, avoid like the plague. All depends on the load you have on the circuit really, shame they didn't record it.
Yes sorry your correct ,so one of the circuits would still be over
 

Reply to High zs on low bay lighting circuits in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
493
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock