Discuss Honeywell 2 amp fused connection unit in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
0
Just a quick questiin can i use a 3 amp for a 2A fused connection unit the factory manuel is saying 2 amp full stop is this 100% or can i use a 3 amp i would of thought this would be sufficiant and then wired to a 6 amp breaker? Never done a alarm system before so making sure as dont want to pop any components
 
If the manufacturers specify 2 amp then yes that is the size you need to fit, fitting higher could damage the electronics under overload or fault conditions before the fuse operates. The 6amp at the breaker is protecting the cabling you wire to the fused spur... are you sure the 2amp is not applying to internal fuses in the panel itself, usually they do not ask for a 2amp in the fused spur supplying power to the unit thus 3amp will be fine... open the panel up, normally there is a fuse as part of the incoming terminals.
 
Hi yes thank you for replys its a new install not repair and deffo not fuses inside ask for 2 amp non switched spur it says switch spur but i prefer to use non switched spur children and all that
 
If you are a spark, best "open" up your profile so people can see your experience

As for fuses, as others have pointed out, you can buy 2A fuses (and others) so buy a few packs for your stock...
 
honeywell are wrong saying to use a sFCU. should be unswitched. so they're probably wrong about the fuse size also. i've been installing alarms since 1981 and without exception, all call for a 3A unswitched FCU.
 
honeywell are wrong saying to use a sFCU. should be unswitched. so they're probably wrong about the fuse size also. i've been installing alarms since 1981 and without exception, all call for a 3A unswitched FCU.
I agree with this.

There is a fuse within the panel that protects all the equipment and a 3A fuse should protect your flex to panel perfectly fine...
 

Reply to Honeywell 2 amp fused connection unit in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
838
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
497
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
448
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
879
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock