Discuss How the CPCs are connected? How would you code the fuseboard? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi guys.
Can someone explain what is this? Where are the CPCs connected? I think the black cable connected to the MET have something to do with it.How would you code that?
 

Attachments

  • 20221021_181540.jpg
    429.7 KB · Views: 37
  • 20221021_181549.jpg
    468.3 KB · Views: 37
  • 20221021_170544.jpg
    426.4 KB · Views: 37
  • 20221021_173438.jpg
    536.8 KB · Views: 36
That is an MEM red spot board I think the conduits are the earth if they are metal!
I took one of those out only 2 weeks ago and swapped it for a Fusebox!
I agree with @loz2754 should check at the sockets and lights / switches if the conduit is continuous,
 
The CPCs are the metal conduits.
If there is continuity to the each point on the circuit, then no code. Otherwise C2 for lack of adequate CPCs.
The black earth wire may be the earthing conductor, but this will need confirmation.
No cpc continuity on 75% of the accessories , you're right. But now what is the remedial action for that?
 
That is an MEM red spot board I think the conduits are the earth if they are metal!
I took one of those out only 2 weeks ago and swapped it for a Fusebox!
I agree with @loz2754 should check at the sockets and lights / switches if the conduit is continuous,
Did you swap the CU only or did a full rewire? And if CU only, did you use the same metal conduits for CPC?
 
@zvspark said
Did you swap the CU only or did a full rewire? And if CU only, did you use the same metal conduits for CPC?

I was very lucky someone had already pulled in a separate earth conductor and insulation resistance were all still good! I guessed that the installation was rewired in the mid-late 80's but for some reason the cu was not upgraded!
 
The CPCs are the metal conduits.
If there is continuity to the each point on the circuit, then no code. Otherwise C2 for lack of adequate CPCs.
The black earth wire may be the earthing conductor, but this will need confirmation.
Are the conduits joined througout the installation?? maybe they hsve used the conduits for cps
 

Reply to How the CPCs are connected? How would you code the fuseboard? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
578
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hi guys. Fuseboard looks fine, but all neutrals are connected at one point outside the fuseboard. That way both rcds trip on fault on any of the...
Replies
14
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
407
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
425

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock