When is your installation date
Well it was last Friday, but I stopped them half way through when I discovered the problem. I am waiting for them to come back with a proposal inorporating Solar Edge + optimisers today, then when I have made a decision (the alternative being to revert to the quoted Growatt inverter wired 8+8 or 6+10) I will ask for next Friday since I will be home then. Friday 13th. Gulp.
 
Last edited by a moderator:
What modules have they given you, sorry I havnt been following what the issues were.

It's in the first post:
"I was quoted for a Growatt-3600MTL with 16 Suntech STP 245S panels. We have a large roof, but it is hipped, so the installer proposed 12 panels on the house roof and 4 on a garage roof with same orientation and similar roof elevation. I did a bit of research on the inverter, even had a reply from Growatt saying that the panels should be connected 8 + 8.

So, today they came to install. The electrician has done all the internal wiring but they need to come back Monday to finish the panels and complete the electrical side.
2 Problems:
1) I just looked at the inverter in the attic and found it is not Growatt, but Samil SR4K4TLA1 (also badged Solar River and also known as Samil 4400w)......"

Might get back here at lunchtime
 
sounds like growatt prefer balanced strings for there inverters were possible, ive just seen some pics on here and i would make them re doo the work as they dont know how to install neatly!!! also we fit suntech 250s so why cant they 12 modules would get you 3kw but the 4 on there string not sure if that will work, also the board the inverter fixed too is not fire retardent is it, these clowns dont know how dangerous DC actually is.

you should speak to the manufacturer of the inverter to see if 1 string of 4= 980w will work


also dont pay them until everything is working and most of all LABELLED
 
Last edited by a moderator:
Is there a regulation thar says an inverter must be mounted on a fire retardent board.

I read a document from SMA that claimed that in theory the constant heat from an inverter will over time dry out wood and could cause a fire. But they concluded the heat from their inverters still would not be enough but were still concerned about wood dust which can ignite at lower temperature.
 
It is good practice to install on a fire proof board, especially when installing in a loft. We use it for every job except if we're on a non-combustible surface. Only trouble is it's not so strong so will usually need to be backed up with ply on the reverse side.
 
I finally got a revised price from the installer - it was going to cost an extra 10% of the total cost to go for Solar Edge + 16 optimiers, so I have decided to stick with them removing the incorrect inverter and installing the one they quoted for - I don't think I would have got the return on that 10%. They are also going to mount on fire retardant board and do proper labelling.
I have given them this question (paraphrasing some of the advice from here - I hope I phrased it correctly):
"We will have 4 panels on the 35% garage roof and 12 panels on the 30% house roof. I know that we should not have these wired as 4+12 into the 2 MPPTs as the 4 would not generate enough voltage. We have talked about wiring the panels as 8 + 8, but with the roof pitch difference, I believe that it would be better to wire as 6 +10 as this would reduce the losses because 10 panels would not be affected by the pitch difference."​
 
If I were you I would check with inverter manufacturer technical helpline just for peice of mind as you seem to be doing the installers job for them
 
New posts

Reply to I am a new PV householder - advice please. Unbalanced strings and wrong inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi all, I hope you can help me please. I had solar system installed nearly 2 months ago and my installer turned out to be cowboy despite having...
Replies
14
Views
5K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
F
A few weeks ago, I had my solar panels remove from my roof and then replaced. Sadly, on removal, one panel was warped and on letting the fixing...
Replies
1
Views
2K
Hi All got call out to a domestic fault on consumer unit totally separate from the job & client mentions to me that they had Battery storage...
Replies
30
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock