Discuss In line fuse holder in the UK Electrical Forum area at ElectriciansForums.net

Yes. BS1362 plug which has to be removed to put on the unfused 5A plug. Therefore quite likely a .5mm cable being protected by a 10A ocpd
 
Yes. BS1362 plug which has to be removed to put on the unfused 5A plug. Therefore quite likely a .5mm cable being protected by a 10A ocpd
Are you missing something, do you seriously believe the cable is going to be subject to overcurrent conditions.
 
Hi Westie - Overload current agreed no prob. But perhaps manufacturer's cable not sized to trip mcb under all fault currents, which may be why they put 3A fuse ?
 
Using the adiabatic eqn and Wylex i2t data sheet for their 10A B type I get 0.5mm is good for about 1200A of fault current. This calc has a 12:12 warranty - 12minutes or 12reads :)
 
Hi Westie - Overload current agreed no prob. But perhaps manufacturer's cable not sized to trip mcb under all fault currents, which may be why they put 3A fuse ?
Yes is possible but the manufacturer has to fit a plug and for this country it is going to be a 13A plug. OP you could try the 5A plug from MK part no. 643WHI which comes with a 5A fuse but you could probably change it for a 3A. I would guess it is a BS646 fuse.
 
Yes is possible but the manufacturer has to fit a plug and for this country it is going to be a 13A plug. OP you could try the 5A plug from MK part no. 643WHI which comes with a 5A fuse but you could probably change it for a 3A. I would guess it is a BS646 fuse.

Now I like that - not seen them before. There's your answer then OP.

Daz
 

Reply to In line fuse holder in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
440
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
886
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
974
  • Locked
I read once, never seen one for sale, that there is a solid brass replacement for the standard 13A fuse in a 13A plug. This is to eliminate the...
Replies
162
Views
12K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock