Original Post.If i do an eicr before i change a consumer unit WHY do i still have to do an installation cert after changing the board?
What regulation says you must do an installation cert after changing a board?
Good practice guide says you should do it but im only asking why i should Have to do an installation cert after i have done an eicr which is more thorough and i havent installed any circuits.
Am I missing something? Do you do a completion cert and a conditions report?You've installed a CU or had you forgotten that.......
Sorry but there's no getting away from it, at minimum I always do resistance insulation tests so I know what faults are likely to exist before introducing RCDs/RCBOs as part of the new CU, and then a full EICR after the CU installation. All of which is covered in my price for the job.
I think the problem is ipf is that, most do a few tests to make sure that after the CU has been changed there will be no embarrassing issues of the recently addition of RCDs have not produced any unwanted tripping.Am I missing something? Do you do a completion cert and a conditions report?
I know, Pete. It's just whether they want to pay for a conditions report or not. I've done the odd board change where they don't...so it's a case of noting on the cert that an EICR is recommended for the existing installation.I think the problem is ipf is that, most do a few tests to make sure that after the CU has been changed there will be no embarrassing issues of the recently addition of RCDs have not produced any unwanted tripping.
The problem as I see it is once you have changed the CU you do an EIC on the work you have done. i,e, change the CU, that leaves the existing circuits IR tested at the least but nothing else tested, continuity, Zs, R1+R2 where applicable, cpc continuity and main bonding, although some will question the bonding issue, so the question is, how do we approach a CU change?
The consensus is an EICR is the best way forward prior to a CU change, if however the client won't agree to paying for an EICR prior to a CU change, then an EIC for the CU change is all the client will get, I feel a change in the method/rules is in need of clarification, mind you there will be some who disagree with this, hence my statement of the need for a rule change.
Even if you did copy the EICR results you would still need to issue an EIC and building control notification for the works carried out
Should that person be touching electrical work, probably not.
Is there legislation to stop him, definitely not.
You do an EICR first because you should do an inspection and test of the installation and remedial work if necessary, before a new CCU is fitted. The EIC is used for notification, using test results after the board change.Why are you doing the eicr first?
You do an EICR first because you should do an inspection and test of the installation and remedial work if necessary, before a new CCU is fitted.
Would be a good starting point , but what if the client wont pay for an EICR, just wants a new CU (a daft scenario I know) I would always ensure I did an IP test at the least to prove to myself that there will be no surprising RCD trips to make my day into a bad day. The EIC will be for the work the Electrician has done i,e, change the CU.You do an EICR first because you should do an inspection and test of the installation and remedial work if necessary, before a new CCU is fitted. The EIC is used for notification, using test results after the board change.
Wrong. For starters, there is no guarantee that those results will be the same (due to alterations, maybe). If a client wants a change of CU only, that's the job, not remedial work recommended. Don't forget that, by installing rcd protection, at the very least, the safety of the installation is being improved.You do an EICR first because you should do an inspection and test of the installation and remedial work if necessary, before a new CCU is fitted. The EIC is used for notification, using test results after the board change.
Goes without saying IMO (on here, that is). Anything serious is either obvious or is going to be found during testing, anyway.This is included on all my CU change estimates:
"NB: If problems are detected during the fuse board change additional work may be required. Such issues and associated costs will be discussed with you, prior to being implemented"
Never had any comments or complaints about it
Goes without saying IMO (on here, that is). Anything serious is either obvious or is going to be found during testing, anyway.
Even have it printed on your tie, then?My caveat ensures that the client understands its not a fixed price!
Cravat mate Cravat spelling on this Forum is atrochousEven have it printed on your tie, then?
Sorry mate, excuse me french.....do you mean that posh fishy stuff..?Cravat mate Cravat spelling on this Forum is atrochous
What an artichoke?Sorry mate, excuse me french.....do you mean that posh fishy stuff..?