I understand that but by adding what u have listed would improve the safety of the installation. Having done the eicr , you would know that the final circuit are ok and by adding rcd protection your maximum zs would be higher.
Charging for 2 certs to change a board wont get many jobs
 
If you are changing consumer units you should understand the requirements for certification for the job. This seems to be a problem of your own making trying to do a full EICR and a CU change in the same day.
You can ascertain the information required for swapping a CU without doing an EICR.
 
What regulation says you must do an installation cert after changing a board?
Good practice guide says you should do it but im only asking why i should Have to do an installation cert after i have done an eicr which is more thorough and i havent installed any circuits.
 
The eicr being a report on a existing installation will reference the protective devices that exist at the time of inspection,renew the board and its all changed
You are required by the regs to issue certification for all installation work carried out,this can be in the form of a minor works or a installation certificate

Reporting the condition of a installation that has been altered can in no way absolve you from the breaking of the regulations by not issuing certification
Reports and certificates are 2 different animals
 
What regulation says you must do an installation cert after changing a board?
Good practice guide says you should do it but im only asking why i should Have to do an installation cert after i have done an eicr which is more thorough and i havent installed any circuits.

631.1
 
The reason we issue EICs when changing CUs, is because BS7671 requires us to do so.
Failure to issue said EIC would mean that the work does not comply with BS7671.
The reason people record test results for the existing circuits when they change a CU, is because they like to fill in all the blank boxes.
Of course if changing the CU entails replacing or installing RCD/RCBOs, then tests of the RCD/RCBOs will be required.
 
An eicr first to find out whether your installing a board to supply a load of circuits that are dangerous or can cause nuisance tripping etc
Why? After basic testing and checking before changing a CU, the installation becomes an EIC. If the client doesn't want a full test you just record it and advise one.
 
I do installation certs for new board changes. I’m not looking for some robot to quote regs at me. By replacing the cu with an rcd board i am improving the safety so why?? Do i have to do the same test again to get the same results
 
If you've already done a full EICR on the property, the only additional tests apart from identifying the new circuit layout would be the RCD tripping times. As you would have already recorded test results from your previous inspection
 
same results only difference is rcd times. All im saying is does no one else think its a bit overkill to do the tests again. Regs are just a guide not an act

Repeating the tests is a different matter entirely to your original question, which was do you need to issue an EIC, which you do if your installation is to be compliant with the regulations.
If of course you just view the regs as a guide and are not to be followed then you have wasted your time by even asking this question in the first place. Just carry on as you feel and ignore the regulations.
 
Well you would still need to provide a cert identifying that the RCD's were faulty, when you've already provided an EICR which will detail that there was no RCD protection installed for the installation.

Basically, you should go back an test/certify the board change
 
If you've already done a full EICR on the property, the only additional tests apart from identifying the new circuit layout would be the RCD tripping times. As you would have already recorded test results from your previous inspection
It all depends on whether you've been asked to replace a CU or to carry out a condition report....the result of which recommends a replacement CU.
 
The point of certification, is to detail what work has been conducted, to record appropriate test results, to confirm the work conducted satisfies the Regulations and to state the date the work was completed.
 
Yes and did what the bpg said because the reasons they gave to why it should be done i agreed with because i want to know what the installation im going to put a new board in is safe. Doing the same thing again after i dont agree with
 
I think the main issue was about the certification. As you said your doing and EICR and not an EIC certificate. The thing is the works carried out has to be certificated and notified so the client has all relevant documents identifying the WORKS YOU CARRIED OUT and not an EICR which is simply a report on an existing installation
 
I think the main issue was about the certification. As you said your doing and EICR and not an EIC certificate. The thing is the works carried out has to be certificated and notified so the client has all relevant documents identifying the WORKS YOU CARRIED OUT and not an EICR which is simply a report on an existing installation
 
Yes and did what the bpg said because the reasons they gave to why it should be done i agreed with because i want to know what the installation im going to put a new board in is safe. Doing the same thing again after i dont agree with

Like I said then, just do what you feel like. You just need to inform your customers that your installations don't comply with the regulations because you know better that their silly requirements. They should be fine with that once you explain you just ignore the bits you don't understand.
 

Reply to Install cert required if eicr has been done in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
I need to do an eicr on a property, but the consumer unit is comercial with contractors on a 3 bed house .is this allowed on a domestic property...
Replies
4
Views
767
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
883
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock