Hi, neighbour has asked me if I would move his cooker control switch for him. Since new position of it is further away,this would require joining existing cable via JB or, as is preferable, running a new cable. Running a new cable is a fairly big job,so do the regs allow a JB to be used in this case. Cable is twin and earth 6mm. Thanks
 
I needed to join a cooker circuit today, due to moving a consumer unit. I used a Wago IP68 box, which is rated up to 41A (with appropriate connectors).
upload_2019-1-26_18-27-24.png

I put two glands for T&E in one of the flat sides. The box is somewhat overkill for where it was going (bungalow loft) but was fairly quick to fit.

Screwfix sell them, see: https://www.NoLinkingToThis/p/wagobox-ip68-junction-box/7553R
 
I needed to join a cooker circuit today, due to moving a consumer unit. I used a Wago IP68 box, which is rated up to 41A (with appropriate connectors).
View attachment 47415
I put two glands for T&E in one of the flat sides. The box is somewhat overkill for where it was going (bungalow loft) but was fairly quick to fit.

Screwfix sell them, see: https://www.NoLinkingToThis/p/wagobox-ip68-junction-box/7553R

60A Click coffin would have been good for that job

60A Junction Box - https://www.toolstation.com/60a-junction-box/p98775
 
I needed to join a cooker circuit today, due to moving a consumer unit. I used a Wago IP68 box, which is rated up to 41A (with appropriate connectors).
View attachment 47415
I put two glands for T&E in one of the flat sides. The box is somewhat overkill for where it was going (bungalow loft) but was fairly quick to fit.

Screwfix sell them, see: https://www.NoLinkingToThis/p/wagobox-ip68-junction-box/7553R
Best post so far for good advice IHO, think thats the way I,ll go. Appreciate all replies.
 
Oh yes you can wago box And they even do a wogo box XL now

The Wagobox XL is only rated to 32A and connectors up to 4mm2. I've used these and found them really more suited to lighting circuits, instead of having 2 or 3 smaller boxes. The larger connectors won't fit into the internal slots.
 
You can fit the push fit red wago connectors into a standard wago box, they are rated to 41 amp it is a bit of a squeeze though. The 6mm cable will go into a standard wago if you remove the black cable grips (which you don't need with a 6mm cable as the side grips hold it in place) However I have used the click boxes in the past which are also good.
 
Got any photos? Not a product I know but the name rings a bell.

One I found while clearing out the van today.

2019-01-27 13.39.55.jpg
2019-01-27 13.40.18.jpg


The two halfs push and twist together, then can be secured with a cable tie round the middle to prevent tool-less opening.
Cables enter through the ends, which are also threaded 20mm holes, then can be secured with cable ties with the struts at the ends.

Great product. Shame they didn't last.
 
I remember them now! Used to see them advertised, but have never used one. I still prefer the 60A junction box though. MK do a nice 30A junction box that will accept 4x 6.0mm cables. Neither are MF though.
 
Will that still be considered MF ipf? like the idea, but just questioning the vaugeries of the rules.

No, but a crimped connection doesn't require an MF enclosure, it is one of the alter alternatives for an inaccessible connection.
If I remember correctly the options are:
MF joint
Crimped connection
Soldered connection
Resin encapsulated connection
 
Use Ashley J803 0r 804. Bin the connectors inside and replace with insulated through crimps. Complies with regs. Maintenence free, cables secured against strain at their terminations, non flame propogating enclosure. However I only use this method if it's really hard to rewire. Rewire is the safest option. If the neighbour has won the lottery you could fit an AFFD and sleep soundly LOL
 
Use Ashley J803 0r 804. Bin the connectors inside and replace with insulated through crimps. Complies with regs. Maintenence free, cables secured against strain at their terminations, non flame propogating enclosure.

Not so sure about that, altering a manufactured product to suit.

Reg 526.3 (vi) Equipment complying with BS5733, for a maintenance free accessory & marked with the 'MF' symbol & installed in accordance with the manufactures instructions.

Connexbox only give their Wagobox an MF status, when using their Wago 222 and 773 connectors.

Altering the Ashley box, as suggested, would not keep its MF status, IMO.
 

Reply to Joining existing cooker cable in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock