Not deemed a suitable luminaire coupler according to 7671 either
Discuss Joining existing cooker cable in the UK Electrical Forum area at ElectriciansForums.net
Install them well and properly and the cables won't move. Plenty just can't do it.....from what I find.I agree that the 20 amp junction boxes are accessible. However they have no cable restraint and are meant to be fixed in place.
With respect. Have a gander at some I did forty odd years back.....not the slightest problem and never had any.Have a gander at Reg 559.5.1 to see what are correct luminaire couplers.
I needed to join a cooker circuit today, due to moving a consumer unit. I used a Wago IP68 box, which is rated up to 41A (with appropriate connectors).
View attachment 47415
I put two glands for T&E in one of the flat sides. The box is somewhat overkill for where it was going (bungalow loft) but was fairly quick to fit.
Screwfix sell them, see: https://www.NoLinkingToThis/p/wagobox-ip68-junction-box/7553R
60A Click coffin would have been good for that job
60A Junction Box - https://www.toolstation.com/60a-junction-box/p98775
Best post so far for good advice IHO, think thats the way I,ll go. Appreciate all replies.I needed to join a cooker circuit today, due to moving a consumer unit. I used a Wago IP68 box, which is rated up to 41A (with appropriate connectors).
View attachment 47415
I put two glands for T&E in one of the flat sides. The box is somewhat overkill for where it was going (bungalow loft) but was fairly quick to fit.
Screwfix sell them, see: https://www.NoLinkingToThis/p/wagobox-ip68-junction-box/7553R
Got any photos? Not a product I know but the name rings a bell.Really miss the Line eggs. I still have a couple rattling about somewhere.
Wago do 6mm connectors but I dont think 2x 6mm cables will fit into a wagobox. Crimp or solder connections.