Hi guys, I'm getting to the 2nd fix stage at long last. I've taken advice from this forum and decided to fit fire rated LED's throughout the house. I've never installed LED's before and usually in the bathroom I would fit a batten holder or a ceiling rose with a HO skirt on! Going back a bit! Question is, are there any restrictions fitting LED's in bathrooms? They are all outside any zone areas. However my concern is the one above the actual shower area. I'm thinking about the environment to which it and possibly others are being subjected to. Any thoughts Gents? Thanks
 
above shower i'f fit an IPX4 or better, no matter whether it's in a zone or not.
 
above shower i'f fit an IPX4 or better, no matter whether it's in a zone or not.

Could I tell the customer that the fittings he supplied are not suitable for purpose and do not comply with BS7671? As opposed to it would be better to go for a IPX4? Don't get me wrong, I agree with both of your recommendations. I'd rather be safe than sorry. Belts n braces with safety pin.
 
Any one know the make of LED light fittings that use the green click male / female type connections? I've only seen them once and all info at home. The ones that i have to install require a 65mm hole.
 
Could I tell the customer that the fittings he supplied are not suitable for purpose and do not comply with BS7671? As opposed to it would be better to go for a IPX4? Don't get me wrong, I agree with both of your recommendations. I'd rather be safe than sorry. Belts n braces with safety pin.

If the fittings are not fit for the environment they will be used in, then they will not meet the requirements of BS7671. It is your professional judgement that will decide whether they are fit or not.
 
I fit IPX4 light fittings as standard in any area in a bathroom.

Obviously the regs call for certain IP ratings within certain zones of the special location. If the lights are outside the zones then they do not have to have any specific IP rating as far as section 701 is concerned.

However the regs also call for equipment to be appropriate for the external influences likely to be encountered in the installed situation. (132.5, 133.3, 512.2).

In a bathroom situation, all equipment will be subject to moisture from water vapour, especially the lighting. You could use the above regs to argue your case of the provided lights not being suitable. In my opinion the same argument could also be applied to the battens and pendants you usually fit too.
 
I fit IPX4 light fittings as standard in any area in a bathroom.

Obviously the regs call for certain IP ratings within certain zones of the special location. If the lights are outside the zones then they do not have to have any specific IP rating as far as section 701 is concerned.

However the regs also call for equipment to be appropriate for the external influences likely to be encountered in the installed situation. (132.5, 133.3, 512.2).

In a bathroom situation, all equipment will be subject to moisture from water vapour, especially the lighting. You could use the above regs to argue your case of the provided lights not being suitable. In my opinion the same argument could also be applied to the battens and pendants you usually fit too.
Thanks...is IPX4 the same as or better than IP65?
 
no. the highere the number, the better the protection. google IP ratings and print off the list.
 
no. the highere the number, the better the protection. google IP ratings and print off the list.

Thanks . had a read etc (whilst at work) so hopefully interrupted correctly......IP65 is better than IPX4. I see many light fittings I have looked at online refer to IP65. Can't recall any saying IPX4. 4 = for water spay.. 5 = water from nozzle.
 
As Tel says, the higher the better. You should be fully aware of the meaning of IP ratings to be quite honest. I should have said IPX4 as a minimum.

I've got a vague idea about IP ratings etc, but I'm not a practicing electrician as such, been out of the game many years. I knew of IP65 but not IP4X. Thanks for reply.
 
Looked on line what customer has brought for the whole house...turns out the fittings are IP44 rated anyhow. Therefore I was worrying about nothing really. I suppose IP65 would of been better though.
 
I've used them, they seemed like excellent kit to me, however they were pretty damn bright! Depends what the customer wants intensity wise.

Well , ! sort of planned it for 3w upstairs when 1st fixing, but just left switch wire in loft ready for 2nd fixing after plastering and holes cut. I decided due to 7w each LED I would put less in. Going to be different story downstairs as I can't get to them. They look OK, neat way to connect them. I did practice fit some 15mm plaster board, found to be very tight in 65mmm hole.
 
JCC love here too.

As a slight aside, has anyone ever used KSR led downlights ? A local wholesaler is pushing them lately.... Apparently a company run by someone who was something to do with JCC. They are pushing them out extremely cheap.
 
JCC love here too.

As a slight aside, has anyone ever used KSR led downlights ? A local wholesaler is pushing them lately.... Apparently a company run by someone who was something to do with JCC. They are pushing them out extremely cheap.
Fitted some ksr led downlights last week.
i think they are on par with the halers one and quite a bit cheaper.
quite a shallow heat sink at the back if space is tight.
 
Fitted some ksr led downlights last week.
i think they are on par with the halers one and quite a bit cheaper.
quite a shallow heat sink at the back if space is tight.

Cheers, I might give them a try then.. :)

I just took a look at some 6w KSRs, £36. I think I'll stick with JCC

I have been quoted a lot less than that.......

I get the ksr non dimmable ones for 18 quid ex vat

About this price in fact :) and about £22 for the dimmable I think
 
By shower rated ones, does that basically mean IP65? I believe when reading manufactures buff on line yesterday, they claimed suitable for bathrooms. Would IP44 be the absolute minimum?
5cebee31c04c2637111de8fe60c89227.jpg
 
I think most electricians would fit IPx4 (or greater) rated downlights directly above a bath or shower even if it is slightly outside the zone (i.e above 2.25m), and then like Murdoch said, you may as well fit them all the same as it will look better.

Unless the ceiling above the shower or bath is going to be subjected to jets of water then IPx4 is absolutely fine.

Here is a good document on IP ratings, I'd read it all Driverman but in particular have a look at pages 8 and 12 and they will explain exactly what all the figures mean with regards IP ratings.

View attachment IPCodes-really good.pdf
 
I think most electricians would fit IPx4 (or greater) rated downlights directly above a bath or shower even if it is slightly outside the zone (i.e above 2.25m), and then like Murdoch said, you may as well fit them all the same as it will look better.

Unless the ceiling above the shower or bath is going to be subjected to jets of water then IPx4 is absolutely fine.

Here is a good document on IP ratings, I'd read it all Driverman but in particular have a look at pages 8 and 12 and they will explain exactly what all the figures mean with regards IP ratings.

View attachment 27287
thats one of the reasons we usd icage, they look the same.

the only difference is a rubber gasket and glass between lamp and twist-lock to hold the lamps in
 

Reply to LED ceiling lights in bathrooms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
773
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
734
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi, I need some advice on the wiring for a new ceiling light. I have taken down the original light, and I'm left with the wiring in the image...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock